were currently doing a job in massive old pub whats going to be a libary, my gaffer says put 10mm bonding to gas and water but how do you actually work out what size is required
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

By selection from BS7671

Section 544
 
Last edited:
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

It depends on the earthing system, the size of the main earth and the size of the supply neutral conductor.
With TT and TN-S, you determine the size required for the main earth using the adiabatic equation, then bonding conductors are half the CSA of the calculated main earth CSA, but no smaller than 6mm².
With TN-C-S, both the main earth and any bonding conductors are sized according to table 54.8 in BS7671, with the minimum being 10mm².
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

ok nice one its having a new mains room so i assume the yeb will install a tncs system
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

just to add to this, i have just finished a apprentiship and i have never been taught about this, we do mainly houses so we allways install 10mm, but i just like to know for my own knoledge
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

just to add to this, i have just finished a apprentiship and i have never been taught about this, we do mainly houses so we allways install 10mm, but i just like to know for my own knoledge

Surely you would have covered sizing of protective bonding conductors at college?
If you havn't got any course notes or reference I am sure we can find something.
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

just to add to this, i have just finished a apprentiship and i have never been taught about this, we do mainly houses so we allways install 10mm, but i just like to know for my own knoledge

Do you not have the On-Site Guide?

Page 27 onwards has it covered.
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

after thinking about what i said, we did get a breif lesson i remember the tutor saying bonding should be half size of the neutral, after just looking in regs it does say this but if you have any notes or links that would be great

why is it half the neutral though and not half x a phase presume sometimes the neutral is different sizes on 3 phase some time, i not had much experience on 3 phse
 
Last edited by a moderator:
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

after thinking about what i said, we did get a breif lesson i remember the tutor saying bonding should be half size of the neutral, after just looking in regs it does say this but if you have any notes or links that would be great

why is it half the neutral though and not half x a phase presume sometimes the neutral is different sizes on 3 phase some time, i not had much experience on 3 phse

Read post 3 and Spinlondons excellent post, in a TNC-S the size of the Main Bonding conductor is proportional to the size of the incoming neutral and is explained in table 54.8 of the regs.

In a TT TN-S system the Main Bonding conductor is sized as minimum to be half the CSA of the Main Earthing Conductor, and must exceed 6mm.

The Main Bonding Conductor is sized for a TNC-S system on the Neutral conductor because it is the PEN conductor ( see the definitions in section 2 of the regs)
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

lol
olo
lol

That is a totally inane post.

The lad is learning and asking questions on here after completing his training, and by posting that drivel as taught him absolutely nothing, except perhaps the merit of your help.

I have to assume you know everything by now and deem this lads question beneath you, if that is the case, perhaps you will refrain from posting such in-depth replies to subjects that are obviously beneath you.

As you have posted just 15 times in 3 years perhaps your best off as lurker status, and leave replies to peoples questions to those on here that wish to help them
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

Hi Chopper, another thing to watch is distance from MET; for example if you're up to 27/28 metres with your bonding 'run' then its at the limit of its required resistance ( <0.05 Ohms ). In this case (if it was,say,35 metres) then you should use 16mm2.

Is that right btw re: the 1/2 the neutral size just for TNCS? Isn't it for TN systems. Or am I wrong again!
 
Last edited by a moderator:
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

Hi Chopper, another thing to watch is distance from MET; for example if you're up to 27/28 metres with your bonding 'run' then its at the limit of its required resistance ( <0.05 Ohms ). In this case (if it was,say,35 metres) then you should use 16mm2.

Is that right btw re: the 1/2 the neutral size just for TNCS? Isn't it for TN systems. Or am I wrong again!

Yes, a bit of confusion, it's sized in PROPORTION to the SUPPLIER'S neutral conductor (not the tails) on TN-C-S systems, and there isn't actually a 0.05 Ohm resistance limit on main protective bonding.
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

Yes, a bit of confusion, it's sized in PROPORTION to the SUPPLIER'S neutral conductor (not the tails) on TN-C-S systems, and there isn't actually a 0.05 Ohm resistance limit on main protective bonding.


and that's a new one on me. is the 0.05 only applicable to TN-S then, IQ?
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

[/COLOR]
and that's a new one on me. is the 0.05 only applicable to TN-S then, IQ?

No, it's only applicable between extraneous-conductive parts as in supplementary bonding, the figure does not apply to main protective bonding.

We had a good thread here around a year ago on this very thing.

Have a look at BS7671:2008 and Guidance Note 3 and you can see where the confusion comes from-the key word is between.
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

If you look on the forms EIC and PIR forms the sections Main Protective Conductors just ask for a "verified connection" and not for a value. As our learned friend posts it is the terminology once again of our beloved regs that throws us.
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

new one on me any links to original thread?
my understanding was bonding should have a resistance upto 0.05ohms (10mm good for about 27metres)

just dug this up from quick search:
bonding serves the purpose of ensuring that no dangerous potential differences can occur. The resistance of such a bonding conductor must be low enough to ensure that its volt drop when carrying the operating current of the protective device never exceeds 50 V

which brings me back to what iq is saying as the above description fits the r<50/ia formula for supp bonding ?
 
Last edited by a moderator:
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

That is a totally inane post.

The lad is learning and asking questions on here after completing his training, and by posting that drivel as taught him absolutely nothing, except perhaps the merit of your help.

I have to assume you know everything by now and deem this lads question beneath you, if that is the case, perhaps you will refrain from posting such in-depth replies to subjects that are obviously beneath you.

As you have posted just 15 times in 3 years perhaps your best off as lurker status, and leave replies to peoples questions to those on here that wish to help them
NO...NO...NO...keep him posting please....as i have much to learn too (which is why i keep coming in here)...but i am sure his wisdom will soon baffle us all..............
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

That is a totally inane post.

The lad is learning and asking questions on here after completing his training, and by posting that drivel as taught him absolutely nothing, except perhaps the merit of your help.

I have to assume you know everything by now and deem this lads question beneath you, if that is the case, perhaps you will refrain from posting such in-depth replies to subjects that are obviously beneath you.

As you have posted just 15 times in 3 years perhaps your best off as lurker status, and leave replies to peoples questions to those on here that wish to help them
He's the first person to successfully make it onto my ignore list!
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

HelloPage 74, GN3, 3.10.3 "detailed periodic inspecting". 4th para down :"When testing the effectiveness of main equipotential bonding conductors, the resistance value between a service pipe or other extraneous-conductive-part and the main earthing terminal should be of the order of 0.05 Ohms or less"Can't see the confusion there...? Am I missing something. Seems clear to me....
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

HelloPage 74, GN3, 3.10.3 "detailed periodic inspecting". 4th para down :"When testing the effectiveness of main equipotential bonding conductors, the resistance value between a service pipe or other extraneous-conductive-part and the main earthing terminal should be of the order of 0.05 Ohms or less"Can't see the confusion there...? Am I missing something. Seems clear to me....

Spartykus, I know what you are referring to here but read it again carefully, where does it say that the resistance of the bonding conductors should be defined?

The measurement is taken between the extraneous-conductive part and the main earthing terminal, you will not find any reference to a resistance limit of the bonding conductors in BS7671 or any of the Guidance Notes.
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

however, the extraneous part ( say water pipe) is connected to the MET by means of it's bonding conductor, so by inference, that bonding conductor must have a resistance of 0.05ohms or less.
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

however, the extraneous part ( say water pipe) is connected to the MET by means of it's bonding conductor, so by inference, that bonding conductor must have a resistance of 0.05ohms or less.

But that's not allowing anything for a parallel path on the extraneous-conductive part....;)
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

It's a poorly written piece-I've got a meeting with Darrell Locke at the IET on 1st November for the Guidance Note 3 amendment-if he hasn't covered it already, I will certainly be drawing attention to it.
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

HI mate get them told wish someone would then there would be less confusion as far as I was aware its below 0.05 as this is what i was taught on 2391 last year and read but now you have said i will have another read properly lol for the umpteenth time
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

:smile5:Morning:smile5:

IQ - Thanks for your patience. I hope you're not too jaded covering something you've clearly been over before, so thanks for bearing with me. I just wanted to understand why you said what you said, as, has been pointed out by several other (learned) members, and time served sparks I know, they all believe it to be so (the 0.05 Ohms or less for the main bond...etc etc). And also, recently, as BruceLee points out, on 2391 courses (was taught this on mine a few years ago too, and it was in all the text books I fervently acquired ....)

HOWEVER! I have stuck with it, re read it, re re read it, and I agree with you!

It is a very poorly written piece of English. Its a tricky language sometimes and to get to the bottom of it (what is written) requires a clear head and a freshly woken up mind.

I have it now. The text does as you say require 0.05 or less between the MET and the bonding conductor. Or other examples. It does not say (As I believed and have been led to believe by lecturers, text books, etc like Christopher Kitchers) that the, for example, disconnected (with a safely isolated installation of course) 88 metre run of 10mm2 main bond from one end to tuther has to be 0.05 or less. At last. I am with you!

You move in higher circles than me btw. I suspect you are a learned fellow. Again, thank you for your patience :mad2:
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

:smile5:Morning:smile5:

IQ - Thanks for your patience. I hope you're not too jaded covering something you've clearly been over before, so thanks for bearing with me. I just wanted to understand why you said what you said, as, has been pointed out by several other (learned) members, and time served sparks I know, they all believe it to be so (the 0.05 Ohms or less for the main bond...etc etc). And also, recently, as BruceLee points out, on 2391 courses (was taught this on mine a few years ago too, and it was in all the text books I fervently acquired ....)

HOWEVER! I have stuck with it, re read it, re re read it, and I agree with you!

It is a very poorly written piece of English. Its a tricky language sometimes and to get to the bottom of it (what is written) requires a clear head and a freshly woken up mind.

I have it now. The text does as you say require 0.05 or less between the MET and the bonding conductor. Or other examples. It does not say (As I believed and have been led to believe by lecturers, text books, etc like Christopher Kitchers) that the, for example, disconnected (with a safely isolated installation of course) 88 metre run of 10mm2 main bond from one end to tuther has to be 0.05 or less. At last. I am with you!

You move in higher circles than me btw. I suspect you are a learned fellow. Again, thank you for your patience :mad2:


It's a poor piece of text that divides opinion but it's one of the points that should really be black and white.

It's often a criticism that BS 7671 is open to interpretation and indeed it is but that is because it is written to be interpreted by competent persons on an infinite range of scenarios that could not possibly all be catered for.

I bet we move in the same circles, the IET just wanted a contractor's input for the Guidance Note amendments ;)
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

It's a poor piece of text that divides opinion but it's one of the points that should really be black and white.

It's often a criticism that BS 7671 is open to interpretation and indeed it is but that is because it is written to be interpreted by competent persons on an infinite range of scenarios that could not possibly all be catered for.

;)

The 14th edition managed it, ...but then that was the last Reg edition that was written in Plain English!! lol!!

Now, since the Reg's becoming a BS, a higher legal form of English has been applied, which can and often does confuse issues, ...ie, open to interpretation. There are quite a few areas where the IEE needs to go through and clean up passages. Many should have been sorted out ages ago, even if it was just as an on-line addendum/correction sheets, that could wait till the next revision issue to be included...
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

Hope this helps, this is an email i sent a while back and one received from the IET.


Hi

Hope you can clarify a issue.

Main protective bonding and its maximum length.

My understanding in general installations TN at 230 v we need a disconnection of 0.4 seconds as part of ADS, bonding needs to be sized as per Reg 544, and as such
there is no restriction upon length, this id due to the fact we have no limit on touch voltage assuming we meet the prerequisite of ADS.

If there is a limit on touch voltage in a general installation which regulation places this limit?

The only limit i see on main protective bonding is that of 415.2.2, this is additional protection and used in locations of increased electric shock. This is shown in Reg
701.415.2 (Note). Where we check the effectiveness of the main protective bonding utilizing 415.2.2.

There is a passage in GN3, though in my opinion the 0.05 ohms is clearly a value for measuring between to points where bonding clamps can not be removed for
example, not applied to the overall length.

Ive looked in GN8, GN5 and BS7430 and i see no limitation other than CSA or when additional protection is required.

Ive spoke to ECA and they are of the same mind, in that in general installation no limit is placed on the length of main protective bonding.

Its probable that many installations have circuits that would drop more than 50v across R2 alone, my understanding is this is ok providing we meet the requirements of
ADS, if additional protection is required then 415.2.2 applys.

Many thanks, hope you can clarify.

Regards Chris


Reply

Hello Chris,

I am required to preface my remarks by saying that I have no authority to interpret the requirements of BS 7671:2008, Requirements for Electrical Installations.
The interpretation of BS 7671 is one of the roles of the Joint BSI/IEE Committee JPEL/64. However, within that constraint, I hope you will find my comments helpful.


BS 7671:2008 does not have requirements that limit the length of a protective bonding conductor. Chapter 41 is based on the fundamental requirements of BS EN 61140 (Refer to Section 410) which includes reference
To the conventional touch voltage limit of 50V. The key technical intent is to meet the requirements for fault protection 411.3 covering protective earthing, protective equipotential bonding and automatic disconnection. Typically you would look to achieve the appropriate disconnection. If disconnection cannot be achieved in the appropriate time then Regulation
411.3.2.6 requires the appropriate supplementary bonding in accrodance with
Regulation 415.2.

GN3 includes reference to 0.05 ohms but this is more to do with proving there is an actual connection between two points rather than making any
Judgement on length. GN3 is currently being updated to clarify this.



Regards
Paul Bicheno
Standards and Compliance
The IET
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

Wow Chr!s wish you'd posted that a few days ago you'd have saved me a few hours trawling thorugh OSG/BRB/GN3/GN8 trying to prove IQ wrong :bigcry::earmuffs:

(just kidding IQ)
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

Where the heck have you been lol?
That puts it to bed :)

Hello IQ, yes its been a while, not had much chance of late to post, hardly stopped for breath lol :)

There is a thread somewhere covering this issue, ill try and find it.

Hopefully GN3 will be a little clearer, its confused many, including a lot of 2391 lecturers who used the .05 figure when teaching students.

Regards Chris
 
Re: bonding gas and water how do you work out when to go up from 10mm to 16mm and so

The thread was "general testing questions" not sure how to place a proper link.

Pushrod had a reply from Richard from the IET, Richard has the job of updating GN3. His reply followed that of many, that of the 0.05.

Since then This has been clarified and the above reply from Paul is the approach which will be clarified in the new GN3.

Regards Chris
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
bonding gas and water how do you work out when to go up from 10mm to 16mm and so on
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
37
Unsolved
--

Advert

Thread statistics

Created
chopper,
Last reply from
Chr!s,
Replies
37
Views
9,341

Advert

Back
Top