Hi
Just doing end to end test
line - line 0.51ohms seems fine
cpc-cpc 0.91 ohms seems fine
But N- N reading is coming up 1.46 Kilo ohms ??!!! any thoughts
I am doing 2392-10 and am fairly green.............be gentle
angus
Dodgy connection.
addition...
Beaten by seconds...again! :-)
Definitely as above.
I have had similar, and all it took was a half turn with the screwdriver to go from about 500 ohm to about 0.45ohm.
Fortunately, it is just this easy sometimes.
Cheers........Howard
it's finding where to use the screwdriver that's the hard part
yeah definatley a bad connection had a line-line the other week when checking for a kitchen fitter, 4.46ish k ohms. Turned out to be a poor connection and burnt out in the back of a socket.
Depends where you're testing.
I&Ting hotel bedrooms once, virtually every room the RFCs had bad readings and just about every socket we removed to look at had loose connections or just pulled out completly. The manager was not happy, only rewired a few years earlier. We left him digging out the installers details.
Not always a bad connection, had it before where the installer had twisted the conductors together and it had broken, giving a high end to end reading. More often than not it will just be a dodgy connection.
Just gotta hope it's at a socket and not a JB under the floor!
Is this a question in theory or something you have just come across in the field?
angus65,
Octopus,