Just a couple of questions...

Exposed connector blocks above ceiling tiles supplying lights etc... C2??

Main 3 phase cut out, tails to Meter for shop, then an old MICC, not terminated into an enclosure, pot exposed and conductors direct to cut out feeding a meter in another part of the building. Now I know it's a DNO problem and I'm ringing them tomorrow but do I need to code this on the EICR? If so C1? It's in a storage area and if anything were to knock the MICC the cables would be likely damaged, or the pot.

Cheers all.
 
Just a couple of questions...

Exposed connector blocks above ceiling tiles supplying lights etc... C2?? Though this contravenes several regs 522.8.4 and 5 and also 526.1 and and 5 unless there was signs of serious strain, damage or heating I would code it a 3, but the NICEIC/ESC have coded it a 2 on their literature, and I guess it would be hard for someone to argue differently against this if anything happened, so yes reluctantly a 2

Main 3 phase cut out, tails to Meter for shop, then an old MICC, not terminated into an enclosure, pot exposed and conductors direct to cut out feeding a meter in another part of the building. Now I know it's a DNO problem and I'm ringing them tomorrow but do I need to code this on the EICR? If so C1? It's in a storage area and if anything were to knock the MICC the cables would be likely damaged, or the pot.

Is this a DNO problem? As I understand your description you have a 3 phase head with tails going to a meter. Is this MICC after that meter? If is is then is would seem to me to be a sub main done by an electrician/contractor. Only reason I ask this in all my years I have yet to see the DNO use MICC cable, it's not their choice of weapon

As for code well again I think you could take the NICEIC/ESC guide and make it a 2. Have you checked though if there is earth continuity? How is the earthing being picked up, ie is there a separate conductor

Cheers all.

........................................
 
Its definely DNO side of meter mate. In fact it comes out of the main fuse carrier, there are also 2 more supplies for flats off the same head however these are in double insulated and fed from henleys again before meter. 3 phase head but only 1 phase used. Again something I think is odd.

Earthing is 6mm cable soildered onto the MICC

Thanks for help mate. I was torn between the code 2 and 3 for con blocks. Regs technically 3 but I usually code a 2. Just making sure I'm not alone

Thanks
Rick
 
In fact I am going back there today so I will take a picture. Like they say, worth a thousand words.
 
Also to add the MICC in question feeds another main cut out and meter within the building. This used to be a seperate building until circa 10 years ago it was knocked through into 1. Customer has specifically requested the board from this supply is a limitation as the server is powered from it as is the comms and can't be isolated
 
Ohhhhhhhhhhhh I think you may have a little hoggy done there mate.

As I said I don't think I've ever seen work done from the DNO in MICC, but true I still haven't seen anything and this may have be the case they have done it this time.

Is the MICC meter an "official" looking one, ie sealed ?

This is either a little "electricity pilfering" or as you say sometime in the past someone as taken a sub main from the main header at the DNO behest to another meter. It will be interesting to see what it is DNO or not the DNO
 
in hackney and bow i have come across many micc mains coming in. i would imagine from 70-80, as micc was the wonder cable then. also the difference between a 2 and 3 is a failure . it is up to you as as the tester to code it as you could argue that the blocks were in good order and mechanically protected by the ceiling .
its now not jusr follow the codes it is up to individual interpretation .
well as i see it any way
 
The main cut out it is feeding isn't sealed, tho not many are as seals have a habit of failing off.

My concern is as to what goes on the sheet and does it need a call from myself to the DNO this morning to get them to come out and assess as with it being pre-meter it is not technically within what I could rectify?

The new EICRs have a section for the supply equipment which I have noted this on, however it needs a code and I need to give the customer a course of action which I am thinking will involve me explaining this to the DNO and not just leaving it to the customer. thoughts?
 
think posting a pic. would be the best. that should get more accurate advice.
 
Trouble is I am off to see client in 20 mins and will need to call DNO etc. Will grab a few pics regardless to cover my back once I have called the DNO. Guess I was just looking for assurance it is a DNO problem and not the customers problem as it is before any metering equipment.
 
All sorted,

didn't manage a pic as my phone battery died however DNO came down, took one look at said "I don't do pyro, will get a subcontract team in".

MICC according to him was used extensively in Manchester between 1960 and 1970 for cables they ran within buildings.
 