F
fjr1300
Hi All
Got a 3 phase 20A per phase supply coming in, feeding 2 gites. The owner needs the 3 phase supply to also feed a new house 66 meters away. The house will only single phase loads and probably be unbalanced most of the time
Now the tables I have, show that for a single phase - the wire needs to be 25mm sq (30Amps max - 83 meters max) but i'm thinking about the neutral wire.
If each phase is limited at 20A and the single phase loads were taking 20Amps - then would the neutral current be 60Amps ?
Is my thinking correct ?
lee
lee