craigday

I recently got called to a rcd kitchen circuit tripping, so I removed all appliances as normal but still tripped so carried out IR test which showed no fault? any ideas no fault found?
 
Disconnect the load and reset rcd, if there's no load and it still trips you need a new rcbo! Hope this helps
 
Sorry just read your reply properly yea carried out all test couldnt find any fault live and dead tests
 
a ramp test would help.
 
IR test again at 1000V. but make sure nothing is plugged in.
 
trapped cable behind an accessory or a nail in cable.. these faults don't always show uo on IR tests. ambient temperature fluctuations cause expansion and contraction, thus the fault is there 1 minute and gone the next. just a case of using the old eyeballs more than relying on test gear.
 