First one I looked at

5.1 A 30mA residual current device (RCD) must be installed in all UK electric and pumped shower circuits. This may be part of the consumer unit or a separate unit.

6 A 45 amp double pole isolating switch with a minimum contact gap of 3 mm in both poles must be incorporated in the circuit.

6.1 It must have a mechanical indicator showing when the switch is in the OFF position, and the wiring must be connected to the switch without the use of a plug or socket outlet.

http://www.tritonshowers.co.uk/media/1180125/aquatronic 3 ultra.pdf

Second one

5. A 30 mA residual current device (RCD) MUST be fitted. This may be part of the consumer unit or a separate unit.

6. A separate, permanently connected supply must be taken from the consumer unit to the Mira Sprint through a double-pole switch, which has at least 3 mm contact separation. The switch can be a ceiling mounted pull-cord type within the shower room or a wall mounted switch in an adjacent room.

http://www.mirashowers.co.uk/onlinecatalog/pdf/1076783_w2_b_mira_sprint.pdf

Where do you get your showers?
 
Good practice regardless, Like I mentioned the other day, a company sending a spark to fit a shower would probably dismiss him if he didn't fit a DP switch, and would do so for sure if he didn't fit an RCD regardless of any loop holes in the regs, this section 7 needs a re-vamp IMO.
 
I'm glad you put this I don't think I could of been that diplomatic and I think I may of got warning number 2 in two days lol
Good practice regardless, Like I mentioned the other day, a company sending a spark to fit a shower would probably dismiss him if he didn't fit a DP switch, and would do so for sure if he didn't fit an RCD regardless of any loop holes in the regs, this section 7 needs a re-vamp IMO.
 
Like I said, I always fit one too, but the regs are the regs and any quarrels over the exact location of a shower isolator are pointless in my opinion.

My only point was that technically they are not a requirement, so positioning is not really a major issue.
 
I know but I see some of the questions and stupid answers on here and think my God, it's as though people are not sure and use this forum to check if they are doing things right, as you and I have said any decent company would send these people down the road, I can understand people asking about something out of the ordernary but these are practacing sparks and IMO should know better
Your hot headed like me, but I have learned to chill, you need to as well.
 
Good practice regardless, Like I mentioned the other day, a company sending a spark to fit a shower would probably dismiss him if he didn't fit a DP switch, and would do so for sure if he didn't fit an RCD regardless of any loop holes in the regs, this section 7 needs a re-vamp IMO.

I wouldn't neccessarily be binning off any of my staff if they didn't fit a shower isolator. It all depends on the situation and what their reasoning was.

Most decent sparks are able to use their knowledge and experience to make an educated and logical decision. We can't all be expected to blindly follow here say and myth.
 
I wouldn't neccessarily be binning off any of my staff if they didn't fit a shower isolator. It all depends on the situation and what their reasoning was.

Most decent sparks are able to use their knowledge and experience to make an educated and logical decision. We can't all be expected to blindly follow here say and myth.

Yep Fair enough Bud, some of us did go through this the other day and I agree with what your saying about sparks using their loaf, however I think clarity over this from the regs needs sorting out, it wouldn't take much to add a bit about isolation in there regarding showers as most decent manufactures insist on them, anyhow just my view, we won't fall out thats for sure, theres no argument, I am just pointing out my view about this.
 
Thanks so much!

I was expecting a torrent of abuse for asking that haha,but better to ask than to get it wrong...

I'm glad that it can go in the cupboard because I've made all the walls good and then the plumber advised to put an electric shower in rather than a mixer due to the new combi boiler.

Thanks again, you lot are stars! Stay tuned for another of my questions very shortly in a separate thread about cooker points... ;)
yes, its just that i wasn`t `on duty` last night....
 
I think if I was the owner of the property I would want to know why an electric shower had been installed when there was a better supply of hot water from the combi boiler.
 
I know but I see some of the questions and stupid answers on here and think my God, it's as though people are not sure and use this forum to check if they are doing things right, as you and I have said any decent company would send these people down the road, I can understand people asking about something out of the ordernary but these are practacing sparks and IMO should know better

KAS1, I hope your better at electrickery than you are at spelling !
 
First one I looked at

5.1 A 30mA residual current device (RCD) must be installed in all UK electric and pumped shower circuits. This may be part of the consumer unit or a separate unit.

6 A 45 amp double pole isolating switch with a minimum contact gap of 3 mm in both poles must be incorporated in the circuit.

6.1 It must have a mechanical indicator showing when the switch is in the OFF position, and the wiring must be connected to the switch without the use of a plug or socket outlet.

http://www.tritonshowers.co.uk/media/1180125/aquatronic%203%20ultra.pdf

Second one

5. A 30 mA residual current device (RCD) MUST be fitted. This may be part of the consumer unit or a separate unit.

6. A separate, permanently connected supply must be taken from the consumer unit to the Mira Sprint through a double-pole switch, which has at least 3 mm contact separation. The switch can be a ceiling mounted pull-cord type within the shower room or a wall mounted switch in an adjacent room.

http://www.mirashowers.co.uk/onlinecatalog/pdf/1076783_w2_b_mira_sprint.pdf

Where do you get your showers?

I think that if you look at the top of that section 5 in the Triton instructions, you wil find:
"The following notes are for guidance only:"
 