This one causes confusion
SNE = separate neutral and earth
The sticker looks fairly recent and I’d put a fiver on TNS
Last time I had this I measured pscc and pefc and found them sufficiently different to conclude it was certainly TNS.
 
The ZE is 0.1 ohms and similar line to neutral , do they use different size cable for the earth and neutral ?
 
Unlike the old TN-S supply cables we expect to see modern SNE supplies will use split concentric cables.
 
  • Like
Reactions: DPG
I was about to say splitcon? In which case you may not detect difference.
I guess next thing is to look at reasons it might mattter since you are below tncs threshold anyway.
Is main earth/bond at least 10mm?
Any relevant special locations or car charger about to be installed?
I see no reason not to believe the sign anyway!
 
  • Like
Reactions: timhoward and DPG
What type of earthing system is this?
Is this in a flat as the red fuse holder would suggest it's a solid link and it's fed from a Ryefield or similar distribution set up
 
Is this in a flat as the red fuse holder would suggest it's a solid link and it's fed from a Ryefield or similar distribution set up
Could be like my flat: TN-S at the head (red link) but seems to be TN-C-S at the Ryefield (actually Lucy) board down in the hallway.

Determining TN-S or TN-C-S by measurement is hard to do. If the PEFC is much lower than the PSCC then it is clear, but on split con cable back to some linked point both N & E are often identical conductors so your measurements will be very similar.

If you have a low-ish PFC, so Ze in the 0.3 ohm or more region, then you have a sporting chance of measuring N-E resistance (with care, power off but at input of isolator, MET not bonded to avoid links via service pipes, etc) to see if it is comparable to Ze (so a long length of N linked to E way back and similar to the estimated L distance/impedance). If you get near-zero then it is clearly linked at the cut-out! Here having Ze near 0.1 is surprisingly low hence my original though about where the N-E link really is (as it is always linked somewhere/somehow).

But as I found in my flat being TN-S at the cut-out is no guarantee that are not really on a PME supply. However, they say SNE so TN-S and unless it is ground floor for EV charger, etc, it is simpler just to go with that!
 
  • Like
Reactions: nicebutdim and UNG
They are flats fed from a Lucy board i am conducting an EICR for the communal areas , just wondered what box to tick ? Although i have been told almost everything is PME at some point these days.
 
They are flats fed from a Lucy board i am conducting an EICR for the communal areas , just wondered what box to tick ? Although i have been told almost everything is PME at some point these days.
You can only tick the box for what you have in front of you
 
If you remove the black X shaped bung you should be able to see if the block is one piece between neutral and earth, if it is you have PME.
 
The notice label to the right of the cut out says PME
 
  • Agree
Reactions: DefyG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
~
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Type of earthing system?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
newfutile,
Last reply from
telectrix,
Replies
12
Views
3,996

Advert