Apologies in advance for yet another Hot Tub TNC-S related thread but I'm just after a few opinions after deliberating for some time on an EICR coding.
EICR at a domestic property was found to have a Hot Tub installed on an outdoor patio which is slate flagstone construction, the hot tub is fed...
So here's the scene
All bonding, impedance values, RCD protection in place.
1) Inside the bathroom outside of the zones a underfloor controller has been installed with no local isolation (wired straight from the board)
I am thinking that its not a code, maybe a note as the only reg i can think...
Hi Guys,
Came across this the other day, a little unsure how to code, I was thinking C3 but would like your thoughts. Obviously been done like this to accomodate different makes of MCB
Evening all..
I have just finished my first EICR! It took a LONG time (10 hours in total - not including writing up the report which I am doing now with a cup of coffee!)
There were many, many faults/problems and I have coded most of them but am stuck with 5 of them and was hoping for some...
Been to carry out a EICR today. consumer a dogs dinner! there are two boards one being an off peak supply. bonding to the gas service comes into the 'normal' unit, water bonding goes into the off peak unit (board now dead) the board is still connected to met.
Im thinking at a push a C2 as...
Interesting job doing a massive eicr on a factory
On a lot of the socket circuits the sockets are wired in singles in metallic trunking with the trunking being used as one of the cpc's it appears.
So two things are the trunking is also being used as cpc for lighting and some other circuits
And...
Fella's
I'm just writing up an EICR from last month, one of the findings was a lighting circuit on the non RCD side of the board where the cpc was used as a strapper in 2 way light switching, Ive marked it as C2 for two reasons, one being that there is no longer a cpc in the cable and also that...
LlandrilloSpark
Thread
cable
coding
conductor
cpc
eicr
however
insulation
live
practice
schedule
Hi all my question is,
What coding is the following.
1. Lighting circuits in property rented to students, circuits chased in walls. No rcd protection.
2. All types of Circuits in a school without rcd protection. Some chased some surface.
Would all above be on a c3 and safe for...
Can anyone give me some advice on coding I recently carried out a EICR on a Commercial premises (communal areas of a block of flats) 3 x DB's all single phase with incoming 3 phase supply with 100A type 2 b fuses with 16mm tails going to each DB - personally I warrant this a code 2 any thoughts...
Hi guys
After advice doing EICR report on a welfare set up on a building site I am after advice on my coding
welfare set up is on a tn-s protected by 100ma main rcd tripping out at 42.3ms at x1 I have some covector heating circuits on a c16 mcb but zs is to high for the c16 what code would...
I need a hand to confirm what coding goes with what please on this house
I have been asked to inspect a house by an agent and this is the situation:
TN-S Earthing (0.4 ohms)
No CPC in lighting circuit with Class 1 fittings
No Bonding to Gas or Water
No Sleaving on any CPCs
All CPCs twisted...
Been doing a few bits at a house down my street. Guy had an EICR done a few months ago (not by me). He wanted the stuff picked up on this put right. Fair enough, I thought. So I had a look through the EICR. The installation is in generally good condition, but I have spotted a few things...
Still trying to get to grips with new EICR coding - got 400 ohms on earth rod all protected by 30mA rcd. What would you code this as under the new EICR?
Hi all,
I am trying to decide on coding for 2 items, and was interested in peoples input, as whether these are acceptable, or C1,C2 or C3.
EICR form
4.3 - Condition of enclosures in terms of IP rating -
4.4 - Condition of enclosures in terms of fire rating -
With both of the above the...
Ok, so here I am testing/inspecting some new floodlights installed at a local community facility. The installers, in their wisdom scarpered without leaving anything resembling a certificate so I'm doing a EICR on the 2 circuits in question.
The "post" end of the circuits is shown here, there is...
I've been asked to go and price a job based on an EICR that the client has had done. Some strange coding in my opinion but just wondering what you guys think?:thumbsup
1shortcircuit
Thread
coding
condition
electric
electrical
electrical installation
installation
review
What would be the best code for sockets that are not rcd protected?
No sockets are outside or near the doors so would it be a code 4?
The supply is a tns with 10mm bonding to gas and water but no rcd protection to any circuits.
Thanks
Looking for some help not came across this situation before, doing pir in domestic property and the consumer unit is old mem type board with rewireable fuses, some have been changed to bs 1361 fuses but the ones that haven't have asbestos flashguard in them. What code would you suggest? Thanks