coding

  1. S

    EICR coding twin and earth tails/riser

    Not unusual in townhouses that have been converted into flats round here to see all the meters in the basement, each feeding a switched fuse spur that then feeds 16mm T+E to each flat. Obviously that's a run of tens of metres, concealed in walls etc with no RCD protection. Guessing it was...
  2. W

    Coding opinion on downlighters

    Ground floor flat, 3 hallway down lighters not fire rated no fire hoods take out a down light and I can look up and see the flat above floorboards C2
  3. Marcus Vaughan

    Coding question - Twin and Earth Tails

    As above really. First time I have seen this but its basically 16mm twin and earth connected straight into the outgoing side of the meter, and into the consumer unit. Quality. Couldn't quite get a picture of the external MET but can confirm an additional cable has been added to bring the size of...
  4. Q

    Eicr coding query

    I am wondering what the installation methods should be for cables run under floor boards and then into stud walls but without thermal insulation...102,103 dont seem relevant and so my understanding leads me to think it would be a cross between c for clipped direct under the boards and then b for...
  5. Dartlec

    EICR Coding Confusion wrt Supplementary Bonding

    Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had been put in place in advance and most of the tests were as perfect as you could get. Seriously, if you wanted to set up a 'perfect' test rig I don't...
  6. J

    Coding for a Ring Final Circuit 1.5/1mm

    Afternoon all, A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD is a 16a type B MCB. All testing has come back as expected for a Ring final that has been installed in 1.5/1mm and the measured Zs is well within max...
  7. B

    EICR Coding for ring ??

    Hi all, just carrying out a EICR with a colleague of mine and fairly new Build house. Install is pretty good all tests came up good with no issues. But we were discussing the RFCs in the house they have 3 installed 1.Upstairs Ring 2. Downstairs Ring 3. Kitchen/Utility Ring We were discussing...
  8. L

    Coding for lack of 30ma rcd protection - TT system

    I’ve had a disagreement with a colleague on this. Installation has 100ma rcd main switch. Some circuits (5) on this side and further 4 on the 30ma rcd side. what is the coding for this?
  9. Q

    Non fire rated downlights and EICR coding&

    Good evening, I am just wondering whether or not non fire rated downlights should be a coded issue (c3 as many electricians have told me) or whether this is false. From memory I believe napit code breakers made it a c3 if there was a room above. P.s I'm still learning and this just seems to...
  10. R

    Help with our debate please on eicr Coding

    Carrying out an eicr and the electric shower casing is cracked on top. My colleague says c3.... I say c2.
  11. S

    EICR coding domestic

    Hello, I'm new to this forum. I'm not quite sure about RCD protection for a domestic dwellings - No RCD protection on circuits where cables are not buried to 50mm - I'm of the opinion its a code 3 however some colleagues are saying its a code 2 ( I cant find clarification on this ) - Any ideas...
  12. Baddegg

    Coding question...

    Got a consumer unit fitted touching a gas pipe on an upcoming eicr,old rewire-able unit, no idea what came first, unit or pipe, but it’s obviously less than the 150 mm mentioned in the on site guide, I know regs are not retrospective but would that come into it in this instance?.....and how...
  13. S

    EICR coding

    Hi guys what would you code a wall light fitting mounted about 300mm away from an oak beamed cieling? The fitting has led lamps fitted but could be replaced with halogen etc?
  14. B

    EICR coding

    Testing on a commercial site which has an outdoor panel which feeds various car chargers and lighting, now upon opening the panel with a triangle key you have access to all switch gear now would you code anything for no secondary barrier? I opened another box and it had a plastic face plate...
  15. B

    EICR coding help

    Is the Napit EICR Codebreakers book any use? Got a few problems that another spark disagrees with, All on one board Plastic board not in an escape route or below stairs C3 No busbar cover on board C3 Spur for Storage heater has crack on fuse holder C3 No cover on inside bulkhead light C3 No RCD...
  16. W

    Codes domestic eicr best practice

    Hi just looking for any tips and knowledge. When carrying out a domestic eicr I’ve noticed a pattern such as often No metal board No rcd protection Not to ip 4x or 2 x I’m still picking up on things to put and don’t want to get into a habit of jut the same ones. Any other recommendations in...
  17. J

    Another coding question

    What code would you suggest for uncovering a power circuit wired in copper cable less than the csa stated in table 52.3 provided the ccc of that cable wasnt effected. Thanks Judd.
  18. J

    4293 elcb coding __________

    Been called to a job for a second opinion, Previous spark said current db set up would warrant a code 2 and therefore need a board change. Granted the elcb set up isn't great for discrimination but cant see this warranting more than a C3. But what about the elcb itself? It Tests out fine. Any...
  19. gazdkw82

    EICR coding (C1,C2,C3,N/A)

    Just doing some mock exams for the upcoming 2391 course. Confused on this question as I got it wrong. Q. If a lighting circuit installed in metal conduit in a shop supplied from a TNS system had no RCD provided for fault protection but achieved disconnection times what would the outcome be on...
  20. S

    EICR coding for transportable unit

    Hi all, I've recently carried out an EICR on a transportable unit and all circuit wiring has been installed in Twin & Earth. According to regs only flexible cabling should be used due to frequent movement, vibrations etc. I myself wouldn't deem this as needing urgent action and think it would...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock