Is the Napit EICR Codebreakers book any use?
Got a few problems that another spark disagrees with,
All on one board
Plastic board not in an escape route or below stairs C3
No busbar cover on board C3
Spur for Storage heater has crack on fuse holder C3
No cover on inside bulkhead light C3
No RCD on any circuits at fuse board garage sockets could potentially be fed for outside use C2
Any advice welcome, will try upload some pics
my opinion, in order.
no code
C2
C3
C2
C2
All on one board
Plastic board not in an escape route or below stairs C3 No code
No busbar cover on board C3 Agree/no code
Spur for Storage heater has crack on fuse holder C3 Agree
No cover on inside bulkhead light C3 C2/C3 depending on type of fitting/situation
No RCD on any circuits at fuse board garage sockets could potentially be fed for outside use C2 Agree
My thoughts in orange.
All on one board
Agree with the codes you’ve done, apart from :
Plastic board on escape route no code unless it is the only means of escape And is not surrounded by a fire barrier C3
Also bulk head light cover unable to say unless I see it. If all live conductive parts are still covered with the cover off then C3, but it could be a C2.
Are these the codes you think or the codes other spark thinks.
Either way what was the difference of opinion.
Where can I get that please mate
Excellent training and reference documents supported by the IET, BSi and many industry bodies
Ok guys sorry have another TT system, no RCD protection at board for any circuit usual lights, sockets, heater, fan
Now would an upfront 100mA be ok I’m not sure of calculation
And would you need a 30mA even if sockets won’t be used for outside use obviously C2 if they are
my C2 for the no busbar cover considered an inquisitive child opening the CU with a screwdriver from his dad's toolbox, or DIY dad opening CU to see if there were any spare ways. potential danger in my opinion.
Got to disagree with that. There is no regulation that supports that view. Live parts are contained behind a cover that is IP2X and that cover is only able to be opened with a tool or key. Fully compliant.
Even if the busbar cover was in place it would not offer IP2X protection from live parts when the cover is off in most CU designs.
Reply to EICR coding help in the UK Electrical Forum area at ElectriciansForums.net
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
6K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
4K