Merlin Gerin is now owned by Schneider and was/is the manufacturer of some of the best off-the-shelf switchgear you can get.
I really like the new PON boards, it's nice the single phase boards are now side hinged instead of bottom hinged too. I hate that they moved the earth terminals to the top though, having 3 layers of terminals in the larger boards is a nightmare.
 
Strange that France has standardised on thirteen module boards and Germany have standardised on twelve module boards, must be a germanic thing about being orderly/symmetrical.
 
There have been multiple configurations of Off Peak / E.7 over the years ranging from DNO switched Off Peak C.U feeding storage / water heating to Dual Rate E.7 meters with no Off Peak switching provided by the DNO for customer use only for switching the meter over.

On the pictured C.U,

Bottom row,, Main Switch (Supplier feed into bottom) Top busbar feeding 4 adjacent MCB AND Red feed to row above. (live 24hr)

Middle row,, Red feed from bottom row into top of 8 MCBs and Busbar. (live 24hr)

Top row,, 4 pole contactor plus 3 single relays.

The contactor will be fed from either a separate customers timeswitch or a fused timed feed supplied by the DNO (nowadays Supplier) near the meter.

The Storage heater circuits will be connected to the contactor and relays, which will be fed from some of the MCBs (labelling not clear).

All MCBs are on 24hr so if your scrapping some or all of the Storage heaters and Off peak water heating, disconnect the feed from MCB to contactor or relay and connect panel heater direct to MCB instead.

If you’re scrapping all Off peak, the contactor and relays can be removed BUT find, make safe and disconnect the timed supply first.
You’ve explained it brilliantly- I have seen storage heaters powered via a contactor before which makes sense when having only the one consumer unit, but I still don’t understand the role of the relays in this configuration- Why are they there when it could just be the contactor, with the load of the contactor supplying the power to the MCB’s during E7 hours?
 
There are only 4 poles in the contactor, with one pole for each circuit. There are 7 off peak circuits (that I can see). Hence the 3 individual relays, one each for the other 3 circuits. There were probably originally 7 of the relays, or 2 of the 4 pole contactors.
You can think of a contactor as a relay with the ability to switch higher current loads.
 
but I still don’t understand the role of the relays in this configuration- Why are they there when it could just be the contactor, with the load of the contactor supplying the power to the MCB’s during E7 hours?
As shown in the Electratec link Oscar21 posted (#21) they were originally all single relays across the top, total number would depend on how many heaters installed, 1 for each heater, 1 for the Top immersion heater and 1 for the bottom immersion heater.
The relays are used as the Electec controller cannot switch the heater loads, it just uses a control signal for the relays.

Sometime in the past some relays have failed and have been replaced by a 4 pole contactor, (effectively 4 relays in one) probably cheaper or happened to be in the van.
 
What usually happens is either the control panel or the brainbox goes kaput, you cant get the spares for them so they need adapting. As you can see the 3 original relays that are left are 2 x immersion ones and one bedroom heater, these will no longer be in use and I think the OP said the immersions are just on a switch now so the relays will have been bypassed, he also said one of the bedroom heaters was now a panel heater so that relay will have been bypassed as well. In fact you can see there aren't any 24V contol inputs to the A1&A2 contacts on the relays anymore.

Whats left is 4 storage heaters (if all 4 ways are in use) but these still need some kind of control so 4 of the relays have been removed and replaced with a 4 pole contactor controlled by a time-clock elsewhere or even the meter itself.

Edit : its 3 storage heaters still in use, you can tell by the labeling.
 
Last edited:
Thought this was sounding a bit familiar.
A thread on the same subject from 2021,,
There's a link to the manual, but no diagrams, in my post #2

 