There have been multiple configurations of Off Peak / E.7 over the years ranging from DNO switched Off Peak C.U feeding storage / water heating to Dual Rate E.7 meters with no Off Peak switching provided by the DNO for customer use only for switching the meter over.
On the pictured C.U,
Bottom row,, Main Switch (Supplier feed into bottom) Top busbar feeding 4 adjacent MCB AND Red feed to row above. (live 24hr)
Middle row,, Red feed from bottom row into top of 8 MCBs and Busbar. (live 24hr)
Top row,, 4 pole contactor plus 3 single relays.
The contactor will be fed from either a separate customers timeswitch or a fused timed feed supplied by the DNO (nowadays Supplier) near the meter.
The Storage heater circuits will be connected to the contactor and relays, which will be fed from some of the MCBs (labelling not clear).
All MCBs are on 24hr so if your scrapping some or all of the Storage heaters and Off peak water heating, disconnect the feed from MCB to contactor or relay and connect panel heater direct to MCB instead.
If you’re scrapping all Off peak, the contactor and relays can be removed BUT find, make safe and disconnect the timed supply first.