If there is blanks missing from a CU what code would this be.
Scenario 1 .. 6 blanks missing from a CU in a corridor cupboard
Scenario 2 8 blanks missing from a locked corridor cupboard
Looking at 3 diffrent reports they have same faults but have been coded differently.
Scenario: Visibly burnt out, entirely blackened, ballast in a fluorescent fitting. Would this be noteworthy during an EICR and if so, how would it be coded? My thinking is that its an obvious fire risk.
Still an apprentice with millions to learn, any input would be appreciated.
Hi all, i'm doing an eicr on a school and am live testing ZS for ring final circuits. The supply is TNCS. i have two results and three questions if i may. i'm getting
c32 rcbo ZS 0.64 ohms. ( Max ZS allowed 0.55 ohms ) Should this be coded a C3 because although ZS fail, the rcd will catch...
Hi All
Writing up an EICR I've been doing recently, wanted to get fellow opinions on coding no identification of conductors throughout, everything's ran in SY cable with no sleeving, so both conductors are black?
As title suggests, how many people carrying out EICR code the use of non compliant cables or at least cables not included in bs7671 for fixed wiring such as SY, YY cables.
I see more and more of this type of cabling used for the fixed wiring to anything as a supply to a socket outlet, to a...
Looking for some advice as im fairly new to EICR reporting, although have passed 2394/95 and have carried out a couple of straight forward reports.
Firstly, on a EICR I have carried out for a family member I have found an old MEM memera 2000 metal clad consumer unit, over 8 years old. I was...
What would the code be on a spur flex outlet, that has the cap missing for where the flex should be? Looks like flex outlet for appliance isn't required and been removed, there fore cap has gone missing.
Picking up reports with it down as C2 and C3.
Any thoughts?
I've been and done an inspection on a rented property today. Normally I am pretty sure of myself with codes but caught myself second guessing today so thought it might help freshen my head up to run a couple of points by the forum for opinion.
First one is a spur from a 2.5mm 32A ring final...
Guys
This is an existing Installation around 12 yrs old RCD protection on the power but not on the lighting, when carrying out a EICR what would the coding be on the lighting in the bathroom?
Evening..
I have just carried out an EICR and I am a little unsure on which code to issue for the following 4 things:
1. The cover has been cut on the fuse box to make way for the plug in mcb's (see picture). I see this all the time. A consumer unit is perhaps the single most important...
I was sent an EICR to comment on....
When I saw the report :
1. CU not AMD 3 compliant - C3
2. Circuits are not identified at consumer unit - C2 (yet the report lists what they are)
3. Cables buried in walls are not RCD protected - C2
4. Lighting circuit serving bathroom is not RCD protected...
Doing EICR on a HMO, DB feeds a Consumer Unit in each room. The feeds to each consumer unit seem to be SWA however the armour is not visible/accessible at either the consumer unit or the DB - it seems to have been cut out behind the DB which is inaccessible.
The cable is buried in the walls and...
Obviously at least a C3, but is it a C2?
Front door opens into tiny hallway, not much more than 1m square with the stairs going straight up virtually in line with front door, approx. 300mm offset to right.
Above you as you enter is a 16th edition insulated CU, tight against the ceiling and...
3ph TT supply into hotel. 300ma time delay rcd protecting a square d qox board. No 30ma RCD protection to any circuits including electric showers. Their is signs of supp bonding in some bathrooms. Thoughts on codes for circuits. Normally pme I would of said c3 for sockets not 30ma RCD...
How would you code the following?
No RCD protection. I coded c2
Not amendment 3 compliant. I coded C3
Meter tails 16mm. I coded C3
Tested the installation and the test results were all compliant with BS7671.
Coding for a 100mA RCD covering lighting circuit on a TT system in a domestic environment?
(Sockets on a 30mA, Ze of less then 50 ohms) (test data left in office along with books, just mulling it over during dinner)
How would you code a cooker isolator switch mounted within the cooker space, I.e directly above the hobs?
It's a metal faceplate mounted flush on metal splash back.
Morning fellas,
Just a quick question if you don't mind,
Doing a EICR and came across what looks like 6mm tails from the meter to the rcd,
iv never seen tails thats small before,
the dno fuse is 60a and its a tt system.
What code would you use please,
Many thanks :)