I did an EICR on a property today and came across a built in hob with a 45A switch but no dedicated cooker circuit
On further inspection it turns out that the 45A switch is spurred from the kitchen socket ring and feeds a double socket at the back of the built in oven. Both the oven and the hob are wired with 13A plugs. This is obviously fine for the oven but the hob is rated at 5.7KW.
From a safety point of view I suppose it is not 'unsafe' as if it were to draw more current than the plug allowed it would simply blow the fuse but its a bit of a bodge for me. The tenant reports it working fine so I can only guess that it never reaches anything like 5.7KW as that would need all 4 hobs on full power.
How would you be inclined to code this on an EICR? I don't see it poses either an immediate danger or a danger under fault conditions due to the 13A fuse in the plug, therefore can only code C3 but what reg would you point to?
I'm tempted to cite 433.1 "every circuit shall be designed so that a small overload of long duration is unlikely to occur" however this applies to circuits themselves so can this be used in this instance?
On further inspection it turns out that the 45A switch is spurred from the kitchen socket ring and feeds a double socket at the back of the built in oven. Both the oven and the hob are wired with 13A plugs. This is obviously fine for the oven but the hob is rated at 5.7KW.
From a safety point of view I suppose it is not 'unsafe' as if it were to draw more current than the plug allowed it would simply blow the fuse but its a bit of a bodge for me. The tenant reports it working fine so I can only guess that it never reaches anything like 5.7KW as that would need all 4 hobs on full power.
How would you be inclined to code this on an EICR? I don't see it poses either an immediate danger or a danger under fault conditions due to the 13A fuse in the plug, therefore can only code C3 but what reg would you point to?
I'm tempted to cite 433.1 "every circuit shall be designed so that a small overload of long duration is unlikely to occur" however this applies to circuits themselves so can this be used in this instance?