Discuss Eicr coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Certainly no code should be attributed to that. Conduit can be used as cpc so long as it tests out and shows no signs of corrosion or damp penetration.
The only thing i will add and have seen so many times is to make sure if the conduit is buried within the building structure any class 1 fittings are securely earth tagged to the conduit back box behind. Seen lots if people fit metal light fittings over the top of the back box and then don't earth the fitting!!
i think you might need to put a sticker on the DB warning the user not to change fittings to class 1 in the future and an observation on the sheet to the same effect
Would only need to do this if the conduit is not suitable as a cpc which doesn't seem to be the case
Reply to Eicr coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
EICR picked up no continuity on cpc on 3 pendants fittings in a grd Floor Flat. Zs measured @ other pendants & complies. Different opinions on the...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
I trained as a electrician in the 70s but have long since retired. Just had an EICR test done on my property in advance of selling. I have a 60s...