I think it's just me and you Sid....
dont dissagree with you, I would also install 2.5mm, its just that the customer has huge amount of 1.5mm and wondered if i could use it.
I know it depends on its inststallation method but what is the max current carrying capacity of 1.5mm swa 3 core?
If im looking at the correct table 4D4A it says 18a clipped direct.
But then this manufactures spec says 32a. (page 3) http://www.alertelectrical.com/upload/pdf/329armoured.pdf
I want to know if its acceptable to run a radial to 2 x outdoor sockets using 1.5mm SWA on a 16a mcb
looks like youve answered your own question then sidI'm with you on this one pevvers..
No one has yet given a valid reason and explained why they wouldnt use 1.5mm SWA on a 16a MCB, or even 20A MCB for that reason.
Ummmm, am I protecting the cable from overcurrents?
Yes.
Whether it be lighting, sockets, FCU's, it matters not as long as the cable and all associated equipment is protected from overcurrents, will disconnect in the required time, etc., etc.
Just because it's 1.5 doesn't mean it can only be used for lighting, just like you could put in 16mm radial circuits for sockets if you really liked, although you would have a hell of a time getting them in the terminals!!
As long as the calculations add up then you are complying with BS7671, which is what I adhere to.
lolI'm saying nuffin...
![]()
Couldnt be bothered to trawl through all the posts so sorry if I'm going over whats already been said.
Do the calcs & if all complies then just use the 1.5mm, nothing wrong with 1.5mm used for sso's if it complies.
Just because the norm is 2.5 don't mean you have to use it after all what size conductors would you use for sso radial circuit if MI was the cable of the day & you are thinking of proffits in the job.
Dont be drawn into this is the norm & this is how we have to do it, thats why your taught how to calculate cable selections![]()
now MI is a totally different ball game, op was for opinions and thats what he gotCouldnt be bothered to trawl through all the posts so sorry if I'm going over whats already been said.
Do the calcs & if all complies then just use the 1.5mm, nothing wrong with 1.5mm used for sso's if it complies.
Just because the norm is 2.5 don't mean you have to use it after all what size conductors would you use for sso radial circuit if MI was the cable of the day & you are thinking of proffits in the job.
Dont be drawn into this is the norm & this is how we have to do it, thats why your taught how to calculate cable selections![]()
now MI is a totally different ball game, op was for opinions and thats what he got![]()
now MI is a totally different ball game, op was for opinions and thats what he got![]()
read my reply, acceptable but not good pacticeThe op was not asking for opinions,
It was asking for the current carrying capacity of 1.5 3 core swa, this is in the brb so no opinion needed.
Also is it acceptable to run a radial in 1.5 swa to 2 x sockets on a 16 amp mcb, again verifiable in the brb so no opinion need.
What you are doing flukey is saying how you would do it, which was definatly not the op.
im not playing pevvers, you can read MY opinionNo **** that is what he got!!
So how comes MI is a different ball game, but SWA with it's higher CCC is not? Surely the same rules apply?
1.5mm MI (bare and exposed to touch, as it would be in this situation) = CCC of 23A light duty and 25A heavy duty clipped direct and 25A light duty and 26A heavy duty on tray.
1.5mm SWA 70 deg c (thermoplastic)= 21A clipped direct and 22A on tray.
1.5mm SWA 90 deg c (thermosetting)= 27A clipped direct and 29A on tray.
Most of the time nowadays I find that SWA is thermosetting insulation, and so the 27A CCC would be the one to look at. Which is better than even the heavy duty MI by 2A... So, with respect, how is MI a different ball game?
P.S. I was being quiet Flukey, but you just wouldn't let it lie!
1.5 MI is a direct replacement for 2.5 t/e in nearly all situations, but then you would know that.But why is MI a different ball game?
Thank God for thatAh, but it has been fun, has it not?
Just realised you only live about 3 minutes drive from me, we should go for a beer and discuss it further!!![]()
beer sounds good, discussing this further doesntAh, but it has been fun, has it not?
Just realised you only live about 3 minutes drive from me, we should go for a beer and discuss it further!!![]()
just down the road from me then, im in pitsea too, small worldI was only joking about the futher discussions....
I'm in Broomfields in Pitsea, but I won't be stealing any business from you as I'm not on the tools anymore!
I would use 2.5 for 2 sockets radialI know it depends on its inststallation method but what is the max current carrying capacity of 1.5mm swa 3 core?
If im looking at the correct table 4D4A it says 18a clipped direct.
But then this manufactures spec says 32a. (page 3) http://www.alertelectrical.com/upload/pdf/329armoured.pdf
I want to know if its acceptable to run a radial to 2 x outdoor sockets using 1.5mm SWA on a 16a mcb
I see 'pete999' wants more info from a 12 year old #2.You got me going there, Pete.
I have a shed [aprox 20 m long] supplied by a swa 1.5 mm coming off a household unit that will only accept domestic 3 pin plug fuses in it, so it is fused at 13 amp & perfectly acceptable by all the posts here. just wondering as my wife does tend to overload things [heater + tumble dryer etc] the fuses have blown beforeSo would I, but I would actually make it an RCBO instead of an MCB.
But a 1.5mm would be fine,![]()
This is a zombie thread. All that matters is that the overcurrent protection for your 1.5mm2 SWA is appropriate for its current carrying capacity based on reference method. Table 4D4A has the CCC of your cable at 21A when clipped direct, or 22A when buried in the ground. Your breaker/fuse needs to be rated lower than this.I have a shed [aprox 20 m long] supplied by a swa 1.5 mm coming off a household unit that will only accept domestic 3 pin plug fuses in it, so it is fused at 13 amp & perfectly acceptable by all the posts here. just wondering as my wife does tend to overload things [heater + tumble dryer etc] the fuses have blown before