I did an IR test on it up to 500v and there was no fault. I did it while it was warm also.OK.
Did you test the heater's whole circuit (i.e. IR it at the CU) or just disconnected the heater to check it alone? Might be nasty cable fault developing otherwise.
I will test but it tripped on other sockets too. That socket is only 6 months old.Have you opened that socket to inspect it? Or try a new one?
It might be the actual act of inserting the plug is causing a fault, maybe N-E so no bang but enough to trip the RCCB.
Will try that. I have IR tested the socket circuit and no issues.If you plug in a big load there, say a heater, then switch the heater on without physically disturbing the socket, is it OK?
Trying to work out if some odd neutral path or similar. I'm guessing you have IR tested that circuit to rule out N-E permanent fault?
OK.I did an IR test on it up to 500v and there was no fault. I did it while it was warm also.
Have you PAT tested what you are plugging in? Maybe faulty plug/adaptor and strain/movement is causing it to N-E short?I will test but it tripped on other sockets too. That socket is only 6 months old.
Hopefully!Will try that. I have IR tested the socket circuit and no issues.
Hopefully, the electrician can work it out tomorrow.
That's a very high leakage. Is that meter accurate down to low mA figures?
So I am hearing this second hand as I was not here, but the spark looked at the DB and the unit's plumed in circuits and they are all okay.
He has stated that I "need to get my equipment PAC tested" and "my equipment is tripping the breaker".
Looks right method, results are bizarre!Am I doing this right? This result expected?
If you IR test that kit you clamped (above) what do you get?I am still going through all the kit in the office doing IR, earth to case and polarity check. No issues so far.
Looks right method, results are bizarre!
The 1mA on the CPC would be reasonable for a floating bit of kit and some filter capacitance.
The 39mA for the L-N difference is difficult to explain and ought to be triggering the RCBO that feeds it.
What is attached to the cable you are testing, has it any external cables such as network or RS232, etc, or is in contact with building metalwork, machines being controlled, etc?
If you IR test that kit you clamped (above) what do you get?
And when doing the IR test try having the CPC/earth also linked to the supply earth at the time.
Edit to add: Have you used your MTF to ramp-test the RCBO from that socket that you are getting 39mA and no trip from?