3kw load...13amp spur...does this comply.
My thinking is that previously it would have but not now.
previously 3000w/240volt=12.5amp....all ok

now stated voltage is 230 not 240
so
3000w/230volt=13.05amp marginally over

but to me it does not comply....even though the actual voltage hasn't dropped,its still at 240 in real life.

This is in a high rise office block that i am testing(new installation)
What are the experts views?
 
Theoretically it may not comply if you are absolutely certain that the 3000W load is 3000W and not, say, 2990W.
A 3000W load (based on 230V) would have a resistance of 17.63 Ω and as you say a current of 13.05 A.
However if this were fed from a 3.3m 2.5mm² cable (or a 2m 1.5mm² cable) the resistance of the cable would be 0.06 Ω and this would reduce the current to 13A as the total resistance from the origin (where the pd is located) includes the supply cable.

Edit: Also based on baker's post a 13A fuse has a near infinite trip time up to about 20-25A.......
 
previously 3000w/240volt=12.5amp....all ok

now stated voltage is 230 not 240
so
3000w/230volt=13.05amp marginally over
It doesn't work like that.

If the 3000W was quoted at 240V then (for resistive load) both the amperage and wattage will be lower at 230V
 
Not got OSG or BGB handy but sure I recall anything over 2kw should be on it's own circuit,
 
What IS the 3kw load?

The load is a 3kw instantaneous waterboiler.(for making tea etc)..and there are about 50 of them being installed in the building.(supplied as a 4mm,20amp radial.)
I'm pretty sure that there wont be a problem,though in the past I have come across burnt out 13amp spurs which were erroneously fitted to control immersion heaters(pre gas days youngsters people used to use them for hot water)
I think they should be using a 20 amp dp(not a big cost difference if any)

Its more the theory I was querying.Says 3kw on the box.
 
The load is a 3kw instantaneous waterboiler.(for making tea etc)..and there are about 50 of them being installed in the building.(supplied as a 4mm,20amp radial.)
I'm pretty sure that there wont be a problem,though in the past I have come across burnt out 13amp spurs which were erroneously fitted to control immersion heaters(pre gas days youngsters people used to use them for hot water)
I think they should be using a 20 amp dp(not a big cost difference if any)

Its more the theory I was querying.Says 3kw on the box.
All is good, then.

I agree with you about the DP switch; the fuse is not necessary.
 
Anytime I've replaced a burnt out spur for an immerser it's been a 20a dp switch that's fitted. Just for that reason of the spurs being too close to the kW rating.
 
It defines it as "The strength of an electric current in amperes".

Are we now going to have ten pages of semantics instead of answering the question?


 

Reply to 13 amp spur in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
G
Hi, (new to forum, first thread) Trying to get my head round voltage drop and using the calcs in practice. I have radial circuit - 16 amp MCB on...
Replies
3
Views
2K
Gloster Boy
G
N
I am trying to find out why an air master tiger 14/60 turbo air compressor keeps blowing the 13amp fuse. MCB does not trip when this happens...
Replies
18
Views
36K
Bobeto
B

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock