Discuss 13 amp spur in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
here goes again 3rd time lucky
3kw load...13amp spur...does this comply.
My thinking is that previously it would have but not now.
previously 3000w/240volt=12.5amp....all ok
now stated voltage is 230 not 240
so
3000w/230volt=13.05amp marginally over
but to me it does not comply....even though the actual voltage hasn't dropped,its still at 240 in real life.
This is in a high rise office block that i am testing(new installation)
What are the experts views?
Theoretically it may not comply if you are absolutely certain that the 3000W load is 3000W and not, say, 2990W.
A 3000W load (based on 230V) would have a resistance of 17.63 Ω and as you say a current of 13.05 A.
However if this were fed from a 3.3m 2.5mm² cable (or a 2m 1.5mm² cable) the resistance of the cable would be 0.06 Ω and this would reduce the current to 13A as the total resistance from the origin (where the pd is located) includes the supply cable.
Edit: Also based on baker's post a 13A fuse has a near infinite trip time up to about 20-25A.......
so
It doesn't work like that.
If the 3000W was quoted at 240V then (for resistive load) both the amperage and wattage will be lower at 230V
Not got OSG or BGB handy but sure I recall anything over 2kw should be on it's own circuit,
What IS the 3kw load?
The load is a 3kw instantaneous waterboiler.(for making tea etc)..and there are about 50 of them being installed in the building.(supplied as a 4mm,20amp radial.)
I'm pretty sure that there wont be a problem,though in the past I have come across burnt out 13amp spurs which were erroneously fitted to control immersion heaters(pre gas days youngsters people used to use them for hot water)
I think they should be using a 20 amp dp(not a big cost difference if any)
Its more the theory I was querying.Says 3kw on the box.
All is good, then.
I agree with you about the DP switch; the fuse is not necessary.
Reply to 13 amp spur in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
6K
G
Hi, (new to forum, first thread) Trying to get my head round voltage drop and using the calcs in practice. I have radial circuit - 16 amp MCB on...
Gloster Boy
G
N
I am trying to find out why an air master tiger 14/60 turbo air compressor keeps blowing the 13amp fuse. MCB does not trip when this happens...
36K
Bobeto
B