A friend is installing a new cooker which has a rating of 16a. The old one was off a 13a fused switch wired on the kitchen ring as it was only rated at 10a. Can a 20a double pole switch be fitted in its place?
 
new one's 16amps then the question is no ,any circuit above 3kw should be on its own circuit so do the calcs 16amps x 230volt = 3.7Kw

I may be wrong nick but isn't the limit 2KW,as I said I may be wrong, can you let me know which reg you are referring to please mine's at work and I'm on the sick with a bad back, old age again.
 
I may be wrong nick but isn't the limit 2KW,as I said I may be wrong, can you let me know which reg you are referring to please mine's at work and I'm on the sick with a bad back, old age again.

Appx 15 (informative) connecting cookers, ovens, or hobs over 2kw on their own dedicated circuit is a general method of achieving compliance with 433.1.103 which states standard arrangements for ring finals and that no part of the circuit should cause the load to exceed that of the CCC of the cable for any long period of time.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
16a cooker switch
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
craigsuds,
Last reply from
dingledong,
Replies
16
Views
6,254

Advert

Back
Top