Please correct me if I have this wrong.
Just looking at the time current charcteristic curves for a 100A BS 1361 fuse (as mentioned by DES) and it shows that said fuse can take a current of around 180 Amps for a time of over 6000 seconds before operating.
6000/60 = 100 minutes . So in theory the installation would have to have a load of over 180A running continuosly for over 1 hr and 40 mins before the main fuse would blow.
Have to agree with DES that 2 showers should'nt pose much of a problem
(unless the house is a hostel for tramps)!