I have just moved in so they stuck with a 6month tenancy - also they asked me to conduct the EICR so they dont have a leg to stand on when it comes to this.

Also all the agents talk around here - if the landlord throws me out then every agent will know within days how bad the electrics are and none of them will touch them. dont think they will go alone with a tenant again as the last tenant they had pulled all walls down, doors off hinges, rubbish everywhere, one hell of a state - hence what led to the work that the landlord did - the house was empty for 18 months before I started renting it
 
Re: 20 Radial Sockets with only 1 T&E cable going to all 20

Not sure if you got this right - why replace all fittings with class one?? - thats metal - class 2 is plastic

Its a house Im renting (I have kids) so I want it correct and not going to take no for an answer - Im just thinking of the 4 months rent free that I will get
Well done for spotting my typo, it's been a long day with my QS... :lol:
 
A radial wired in 2.5 and protected by a 20A MCB is acceptable, as long as the cable installation method does not de-rate the cable below 20A.
There is no minimum or maximum number of sockets allowed.
It's unlikely that the earth conductor is 2mm² more likely 2.5mm², which is the minimum CSA allowed if mechanically protected and PME conditions do not apply.
I take it you haven't any limitations?

the CPC is 1.5mm (standard 2.5T&E cable)

the cable is PVC cable installed in trunking

No LIMs agreed - but all installed in last 18months so all should be under the 17th regs either way - again nothing signed off

Agent told me to do it to current regs anyway


One thing which is nice - all test results are well within range - IRs all over 800MOhms
R1+R2 all low (which I expect as all sockets are a maximum of only 7meters from the CU)
RCD trip times under 10ms (1x and 5x)
 
the CPC is 1.5mm (standard 2.5T&E cable)

the cable is PVC cable installed in trunking

No LIMs agreed - but all installed in last 18months so all should be under the 17th regs either way - again nothing signed off

Agent told me to do it to current regs anyway


One thing which is nice - all test results are well within range - IRs all over 800MOhms
R1+R2 all low (which I expect as all sockets are a maximum of only 7meters from the CU)
RCD trip times under 10ms (1x and 5x)

The radial sounds fine.
You haven't mentioned what the earthing system is?
 
Doing a EICR on a house.

Situation

Radial on a 20A MCB
20 Sockets on Radial
Each socket on that radial has only 1 x 2.5mm T&E going to each socket

Am I right to think that the person who did the work (the landlord) has spared off a JB in above the roof to each socket

From looking at the rest of the house, there are several C1s, C2s, and loads of C3s (4 pages in total) - including no bonding and only a 2mm cable from main earth (TN-S) to CU

Also am I right in thinking this is a C3 as it is not dangerous even if a fault occurs???


OP - 7th Line down - TN-S!
 
Agent told me to do it to current regs anyway

Agent seems to know that Bs7671 requires that the eicr is compared to current regs, but I don't believe for a moment that you needed the agent to tell you that is so nicholas
:D
 
It's likely that after you've spent all your time doing the EICR the landlord will get another sparks who will quote alot cheaper than 4 months rent to do the remedial work....or use thier cheap quote to batter your price down (as they will know it's in your own interests to do the job as your living there).

Personaly i'd be tempted to rent somewhere else that's safer quoteing the fact electrics are dangerous so you want your deposit back with no more payments to be made.

With the Electrics being this bad god only knows what other shoddy work has been done without being notified....especialy in regards to the aforementioned gas boiler and fires.

Pack up,ship out and leggit to a safer home...
 
I just had a full Gas safety check last week - which I paid for (didn't trust the landlords one as it didn't have it all filled in correctly - nor did it have a gas safe number on it)
It failed on 2 things - bonding and the other being the overflow value (which lets out steam) was not going all the way to the floor. - just above head height - would burn someone walking by

There are several over things that needs doing apart from the electrics - replace carpets, replace the drive way (materials supplied by landlord), garden needs dealing with as it is all overgrown - may need ripping up and replanting, holes to be filled on outside wall, replace porch (materials supplied by landlord), repaint the outside (agent doing this)

I was going to do most of the jobs that needs doing for the 4 months rent - payable over a period (say 10 months) so the landlord gets his money every month with a deducted amount - with the condition that I cant be evicted as well - and if I am evicted then outstanding amount is payable immeditally - I dont want to pack my bags and leave as the area is fantastic and the views are worth so much more than I am paying in rent
 
sounds like an awful lot of work for 4 months rent, are you sure its worth it? Also are you going to have a chance to appreciate these views, you will be slogging your guts out .
 
sounds like an awful lot of work for 4 months rent, are you sure its worth it? Also are you going to have a chance to appreciate these views, you will be slogging your guts out .
It was 8 months ago! I would hope he's finished it by now
 
probably moved if it was that bad but prob a bit of a drama queen as well
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
20 Radial Sockets with only 1 T&E cable going to all 20
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
35

Advert

Thread statistics

Created
Spazz,
Last reply from
hasel5,
Replies
35
Views
3,815

Advert