Definitly need rollers on this job.

Using even 200m of 4 core 120mm (can't find the weight for 5 core) cable will weigh just over 1480kg.

Not just damage caused by catching debris in the trench. At that weight, pulling with a tractor without rollers will likely stretch and damage the cable anyway.
End up being 95mm at the tractor end.
[automerge]1567677309[/automerge]
In all fairness to the OP if you have all the correct equipment let us know how it goes.
 
Last edited:
Definitly need rollers on this job.

Using even 200m of 4 core 120mm (can't find the weight for 5 core) cable will weigh just over 1480kg.

Not just damage caused by catching debris in the trench. At that weight, pulling with a tractor without rollers will likely stretch and damage the cable anyway.
Thanks Rob- yes have got a roller organized
 
Rather than pull the cable from a stationary drum and pull it over numerous little rollers wouldn't it be better to move the cable drum along the trench and unwind the cable directly into it? No need for little rollers then..
 
Rather than pull the cable from a stationary drum and pull it over numerous little rollers wouldn't it be better to move the cable drum along the trench and unwind the cable directly into it? No need for little rollers then..

I'll let you try and control rolling something that with the drum included is probably more than 2 tons. I wouldn't want to.
 
I'll let you try and control rolling something that with the drum included is probably more than 2 tons. I wouldn't want to.

You would have to control the drum if you are pulling the cable from it..
I've seen big reels of cables on wheeled units. The OP says he is going to use a tractor. I don't see a problem, if using the right equipment.
 
He needs to decide what is happening with UKPN first before worrying about what size of cable to get.
But before that you need to know what size supply is actually required.
There's no point getting a bigger transformer installed if the current supply will do the job.

To get 100A over that distance I would hazard a guess at 2x 120mm in parallel, but that is just a guess.
Hi Dave did you get my message not sure I managed to send it successfully?
 
Yes I have got your message, I'll reply later whne ive got chance to read it properly.
Hi Dave , you interested in helping ? Keen to move forward. Many thanks Ian
[automerge]1567719741[/automerge]
Hi Dave - you interested then in quoting for this job ? - I notice your answering other threads tonight so can only assume that your not interested in actually quoting for this paid work? Kindest ian
 
Last edited:
What is in this domestic(?) property which requires a 3 phase supply and circa say(tbc) 50A per phase so 230 x 50 x 3 =35 kW? Or is it more than one home? - each with electric heating?
[automerge]1567753765[/automerge]
OP: Would it be practical for your client to have 'load shedding' to allow a lower capacity supply?

For example, there could be arranged 3 types of supply in the property:

a. Permanently on - say for lighting, refrigeration and gas boiler;

b. Timed (and maybe sequenced on) - say for white goods operated overnight and immersion heater (using off peak perhaps);

c. Sheddable - a supply which is only on if demand on other circuits is less than a certain number of kW - say immersion heater element on during the day.

You get the gist.
 
Last edited:
As above, what is the expected maximum demand for this kiosk?
 
Re the cable costs have you looked into doing it in multiple AWAs?
Also why the 5th core? Do you need to an earth conductor?
 
Re the cable costs have you looked into doing it in multiple AWAs?
Also why the 5th core? Do you need to an earth conductor?

I can't imagine AWA being any cheaper than SWA as the conductors won't be any smaller, assuming you mean single core AWA?

We can only assume that the fifth core is for earthing purposes, however I wouldnt be too sure that using what will presumably be TNCS, as its a new connection, on its own over that distance is sensible. The possible difference between the TNCS earth and true earth after 250m could be a bit big.
 
Has the OP had a quote from the DNO for a new supply to the required location? I don’t see this has even been considered, but seeings as the cable and installation is going to cost a five figure sum, I’d certainly want to weigh this up against the simpler alternative which may or may not cost much more.
 
A few years back (2011), installed a 4c 240mm swa with a separate 240mm earth. We hung the reel from a 5 ton digger bucket and unreeled it that way. 105 metres. I think it cost about 8k.
 
A few years back (2011), installed a 4c 240mm swa with a separate 240mm earth. We hung the reel from a 5 ton digger bucket and unreeled it that way. 105 metres. I think it cost about 8k.

240mm earth with a 240mm cable?
 
You would have to control the drum if you are pulling the cable from it..
I've seen big reels of cables on wheeled units. The OP says he is going to use a tractor. I don't see a problem, if using the right equipment.

Rather than pull the cable from a stationary drum and pull it over numerous little rollers wouldn't it be better to move the cable drum along the trench and unwind the cable directly into it? No need for little rollers then..
This method works just fine if the trench and surrounding ground is straightforward. We laid a 240mm 150 mtrs a couple years back using this technique it went really well and was quite simple.

On the other hand pulling a cable of this size can be a different story. Its imperative that you are set up correctly with the correct equipment! We pulled a 240mm in earlier this year. It was only a 90 mtrs run, we hired 35 rollers and a powered cable winch and attachments. It was hard work, very time consuming and very labour intensive, mainly because the run was not straightforward so we had to go slowly and do continual inspections to the sheath. Personally, in the future if I come across anything as / or more difficult as the this last one I'll be hiring the services of a specialist company.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
uk
Website
https://www.foxwoodcamping.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
Business Name
Fox Wood

Thread Information

Title
5 core SWA 120mm pvc cable
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
61

Advert

Thread statistics

Created
buzzer123,
Last reply from
Intoelectrics,
Replies
61
Views
9,442

Advert

Back
Top