Arms
what's your take on adding circuits to a full DB.
Warehouse unit,3p DB,full to capacity,new 3p circuit to be added,client refuses to upgrade DB.
Would you reconfigure a couple of circuits to allow for this new circuit.
 
see if any two lighting circuits can be put into one breaker. sometimes the lighting circuits are split for convenience e.g upstairs and downstairs and it isn't always unsafe to put them into the same breaker. otherwise just tell him you want to do the job properly and if they arent prepared to pay for it then run away
Agree,thanks
 
When he expresses his disgust with shutting down his site for works perhaps remind him that doing it properly this time round and installing a DB with many spare ways will prevent this problem from happening again in the future.

Edit:

Another option could be to consolidate a few 1P circuits into their own DB fed from the exsisting 3P DB. You could move 4 lighting circuits over to a 1P DB and have enough ways for a 3P MCB and 32A SP MCB to feed the new DB.
 
If you’re doubling up a couple of lighting circuits here and there, and maybe a single point spur onto a ring.... you’re going to have to reconfigure a lot of other circuits to get 3 together for a 3 phase circuit.

No bodge job, @cliffed Tell him it needs to be done right. Got to keep those phases balanced and all that.
 
When he expresses his disgust with shutting down his site for works perhaps remind him that doing it properly this time round and installing a DB with many spare ways will prevent this problem from happening again in the future.

Edit:

Another option could be to consolidate a few 1P circuits into their own DB fed from the exsisting 3P DB. You could move 4 lighting circuits over to a 1P DB and have enough ways for a 3P MCB and 32A SP MCB to feed the new DB.
Agree,hopefully go for the new Db
 
If you’re doubling up a couple of lighting circuits here and there, and maybe a single point spur onto a ring.... you’re going to have to reconfigure a lot of other circuits to get 3 together for a 3 phase circuit.

No bodge job, @cliffed Tell him it needs to be done right. Got to keep those phases balanced and all that.
Yea,he’s gonna have to go with the flow.
 
Sub board off the existing board for me, not a henley block. Then move a few circuits over to the new board to make way for the submain breaker.
The OP only needs to install one circuit, if he can gain enough space for an MCB to feed a sub-board he wont need a sub-board!

I think it's rather silly to dismiss the idea of grouping together one or two circuits to gain enough ways, without knowing the loads/circuits involved it may be a perfectly viable option. There seems to be a trend on this forum of late to dismiss common sense solutions to a simple problem as a bodge, and advocate 'walking away' if the client wont pay for the perfect end product. Perfect is not always required as long as a solution is safe, compliant and keeps the customer satisfied.
 
Last edited by a moderator:
what's your take on adding circuits to a full DB.
Warehouse unit,3p DB,full to capacity,new 3p circuit to be added,client refuses to upgrade DB.
Would you reconfigure a couple of circuits to allow for this new circuit.
Ah sorry about my post regarding a 13 Amp socket reread your post and it's a new 3 phase circuit that is required sorry if I confused the issue, my bad.
 
The OP only needs to install one circuit, if he can gain enough space for an MCB to feed a sub-board he wont need a sub-board!

I think it's rather silly to dismiss the idea of grouping together one or two circuits to gain enough ways, without knowing the loads/circuits involved it may be a perfectly viable option. There seems to be a trend on this forum of late to dismiss common sense solutions to a simple problem as a bodge, and advocate 'walking away' if the client wont pay for the perfect end product. Perfect is not always required as long as a solution is safe, compliant and keeps the customer satisfied.
Agree,& that may be the logical way to go,I doubt very much the client is gonna be happy with the idea of a new Db & costs.
If we walk away from it,no doubt someone will do it.
All will be noted on the certificate,so will pass the onus back onto the customer.
 
The OP only needs to install one circuit, if he can gain enough space for an MCB to feed a sub-board he wont need a sub-board!

I think it's rather silly to dismiss the idea of grouping together one or two circuits to gain enough ways, without knowing the loads/circuits involved it may be a perfectly viable option. There seems to be a trend on this forum of late to dismiss common sense solutions to a simple problem as a bodge, and advocate 'walking away' if the client wont pay for the perfect end product. Perfect is not always required as long as a solution is safe, compliant and keeps the customer satisfied.
well said tooth puller ,I could not say better me self.:D
 
Kinda agree,but telling the client & making an observation & written report,given to the client,he too has that responsibility ,& decision making.
Maybe no different from replacing plastic Db’s,or any other “grey area” regulation.
Wirepuller makes a good point,logic & a sensible approach may be the answer.
 
Squeezing in a single phase circuit may be possible ?
But another three phase circuit ?
That's just crazy stuff
Tell him do it right or not at all !
after all if something goes wrong
then YOU wear the can not him.
It may or may not be possible, neither you nor I know the configuration of the existing DB. But to dismiss it without investigation as crazy is just plain daft. There could be a number of MCB's feeding a radial with one socket on the end which could easily and safely be tacked onto a ring as a spur gaining a way. Who knows without checking.
Why is something likely to go wrong with a carefully tested and thought out alteration to circuits in an existing DB? You clearly don't have faith in your own ability to engineer a different but compliant solution to a problem.
'Walk away' is one of the most common phrases on here of late, is nobody capable of thinking of something different?
Apparently not.....We live in Little Britain World.........'Computer says no'......
 
Last edited by a moderator:
There seems to be a marked difference in opinion on this thread than another similar one that I had argued before :

(Does this setup contravene any regs or is it ok? - https://www.electriciansforums.co.uk/threads/does-this-setup-contravene-any-regs-or-is-it-ok.167990/.

For the record, and you will see this from the other thread, I don't believe it compliant to lump circuits together. I asked the NICEIC about the relevant regs relating to this and they agree (albeit they don't write BS7671). My only regret is that I didn't come up with the three phase circuit argument on the previous thread! That would have nailed it I think.
 
22F9B998-F70E-4F18-9A67-3FF501C4CBD8.jpeg


The Niceic should be listened to more than bs 7671 as They are more important and will end up running everything eventually anyway.
You’ve been given the bucket of chum award for the ‘Most likely Bait Post’ of this Thread!
Congratulations, wear it well!
Edit - although that does look a lot like the chilli con carne I made last night!
 
There seems to be a marked difference in opinion on this thread than another similar one that I had argued before :

(Does this setup contravene any regs or is it ok? - https://www.electriciansforums.co.uk/threads/does-this-setup-contravene-any-regs-or-is-it-ok.167990/.

For the record, and you will see this from the other thread, I don't believe it compliant to lump circuits together. I asked the NICEIC about the relevant regs relating to this and they agree (albeit they don't write BS7671). My only regret is that I didn't come up with the three phase circuit argument on the previous thread! That would have nailed it I think.
Nobody is suggesting lumping circuits which should remain individual circuits together, but it is plain stupid to suggest a radial serving a single 13a socket would not be compliant 'lumped' onto a local ring circuit to gain a way. Of course 3 adjacent ways are required here, but my issue with this thread is that the option is being dismissed as a bodge without even knowing the configuration of circuits in the DB. Of course it would be a bodge with a cak-handed approach, but I'd hope a professional electrician could investigate the possibility of accommodating the clients wish for a compliant cheaper solution, and not just throw the toys out and walk away. Far from professional in my opinion.
 
Nobody is suggesting lumping circuits which should remain individual circuits together, but it is plain stupid to suggest a radial serving a single 13a socket would not be compliant 'lumped' onto a local ring circuit to gain a way. Of course 3 adjacent ways are required here, but my issue with this thread is that the option is being dismissed as a bodge without even knowing the configuration of circuits in the DB. Of course it would be a bodge with a cak-handed approach, but I'd hope a professional electrician could investigate the possibility of accommodating the clients wish for a compliant cheaper solution, and not just throw the toys out and walk away. Far from professional in my opinion.
Disagree with the first part of your reply WP
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Adding circuits to a full DB
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
43
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
Dave OCD,
Replies
43
Views
5,787

Advert

Back
Top