Hi all looking for some advice on a job I am doing wiring up the heater of an outside swimming pool.....the heater is 12kw rated 230_v...the pool is about 8 metres away from the mains in the guys house...I am running a 10_mm twin from the mains to a 63amp plug and socket on the outside of his house...from there I am running a 10 mm armoured flex to the heater which sits in a waterproof enclosure at the side of the pool....the problem I have is at the mains...a 50 amp rcbo would have been perfect as the guy has 3 spare ways on the wylex board for the house...but 12kw =52.17_amps!!anyone recommend a small enclosure which would house a 63 amp RCD and a separate 63amp MCB,single phase ,pretty small in size and cheap lol...or any other suggestions for the mains side...cheers in advance people:)
 
BG garage CU. but change the RCD and MCB to 63A. you won't need overload protection as it's a fixed load. just fault protection so 63A is fine, provided that the cable installation method is good for 50A ( 12k/240=50).
 
Cable installation method is fine mate....I have never seen the inside if one if the units you are referring to...will it take 25 mm tails in the top?is the RCD /MCB not where the tails go IN TO?I am thinking I would need a separate mcb for the load side?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice on wiring a heater for an outdoor swimming pool
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
Grumbo14323,
Last reply from
Gnarly,
Replies
5
Views
1,378

Advert

Back
Top