So I’ve recently started my level 3 course and I’m doing electrical system designs the one with the hotel extension and pool and cafe block I’ve done question 1 but stuck on all of question 2 some guidance would be appreciated thanks.
 
Hi everyone, I’ve completed most of the assessment 615 but I can’t find the right wording / fully understand question 10... it’s annoying as it seems like a basic thing to know but my brain is a little fried. Any help would be of huge help!! Thanks.image.jpg
 
Last edited by a moderator:
Upvote 0
You need to understand the difference between isolation and switching. Do you have Guidance Note 2.
 
Upvote 0
I’m stuck on questions 10... seems quite straight but struggling none the less. Anyone able to help?
Think about it logically;

Isolation for maintenance; well that just screams plant room (hazarding a guess at the location of this assignment - Swimming pool?)

Switching for mechanical maintenance; again this screams to bear near any machinery or plant

Functional switching; every room/area within the complex to some degree
 
Upvote 0
Think about it logically;

Isolation for maintenance; well that just screams plant room (hazarding a guess at the location of this assignment - Swimming pool?)

Switching for mechanical maintenance; again this screams to bear near any machinery or plant

Functional switching; every room/area within the complex to some degree
This is great. I need a greater understanding of functional switching will need to read up on that. What’s an example for further requirements?
 
Upvote 0
So I’ve recently started my level 3 course and I’m doing electrical system designs the one with the hotel extension and pool and cafe block I’ve done question 1 but stuck on all of question 2 some guidance would be appreciated thanks.
im the same john stuck on question 2 a 2b right to 2i
 
Upvote 0
2a - Find some lights, print off manufacturers data on said lights

2b - Draw on the positions of the lights

2c - Draw on sockets and FCUs

2d - Draw on each circuit on such a way that a fault with 1 circuit will not affect another

2e - devise a numbering method to ID circuits in relation to the circuit number, room number and/or phase

2f - Draw on any additional distribution boards of you deem th necessary

2g - Draw on lighting circuits in relation to the pool and show switching positions

2h - devise a numbering method to ID circuits in relation to the circuit number, location and/or phase

2i - Annotate drawings with symbols compliant with BS EN 60617.
im the same john stuck on question 2 a 2b right to 2i
 
Upvote 0
does any one have any completed or part done plans for the 2365/5357 drawings to see if I am doing it right
 
Upvote 0
I’m suck with the question attached 615 2365 electrical design project ? question 5 2 hours still can’t work out the answer
 

Attachments

  • 6BF99E20-B011-4A03-81F1-9CC249F10591.jpeg
    6BF99E20-B011-4A03-81F1-9CC249F10591.jpeg
    83.3 KB · Views: 300
Upvote 0
I’m suck with the question attached 615 2365 electrical design project ? question 5 2 hours still can’t work out the answer
Easy method, use the adiabatic equation to find out the size

S = ✓ I^2 * t / k

I = the current required to operate the device
t = disconnection time required for the device
k = factor given for the cable selected - Typically 115

So for argument's sake, let's say we have a fault current of 320 (taken from your trip curves) a time of 0.1 (taken from your device operating times) and a K factor of 115 (taken from the tables following the trip times)

S = ✓ I^2 * t / k
S = ✓ 320^2 * 0.1 / 115
S = ✓ 102,400 * 0.1 / 115
S = ✓ 10,240 / 115
S = 101.19 / 115
S = 10.05

As there is no conductor with a CSA of 10.5, you select the next size up, in this case 16mm^2

The above is purely and illustration and values may not be accurate but it serves to show how to lay out the equation so that you can understand what is going on at each step.

Hope this helps
 
Upvote 0
Easy method, use the adiabatic equation to find out the size

S = ✓ I^2 * t / k

I = the current required to operate the device
t = disconnection time required for the device
k = factor given for the cable selected - Typically 115

So for argument's sake, let's say we have a fault current of 320 (taken from your trip curves) a time of 0.1 (taken from your device operating times) and a K factor of 115 (taken from the tables following the trip times)

S = ✓ I^2 * t / k
S = ✓ 320^2 * 0.1 / 115
S = ✓ 102,400 * 0.1 / 115
S = ✓ 10,240 / 115
S = 101.19 / 115
S = 10.05

As there is no conductor with a CSA of 10.5, you select the next size up, in this case 16mm^2

The above is purely and illustration and values may not be accurate but it serves to show how to lay out the equation so that you can understand what is going on at each step.

Hope this helps
Thanks for this it’s just different this level 3 as I’m dyslexic not with reading and writing but with maths and new things of of my comfort zone
 
Upvote 0