GBDamo

Got called to "a flat in Manchester has no hot water" at 16:30 today and to be frank I was a little miffed to have to attend.

So arrives at site, spends 20mins finding parking, 30 mins finding the site contact, getting keys and then being informed that it was not one flat but eleven.

Have no idea what the supply is, big I'd guess, nor did I have access to ant distribution equipment, just a list of flat numbers.

So I go to the first one. The 16A MCB was off and was informed that "it goes bang if you try to turn it back on" which I took his word for.

So I worked back from the tank, element OK, thermostat OK, wiring OK however the timer was visibly burnt out.

Did a random sample of the other ten and of the four I checked out all had the same burnt out timer.

Due to the time nothing more was done and an assumption (I know?) made that all had blown.

The only other thing I did was to check the local voltages and all were 236-7V and steady, for the brief time I observed.

These flats were all over, not just one floor so unlikely to be from a single phase or distribution board.

The tennants all made the same complaints of flickering lights and one long recent power outage.

None of the staff had any knowledge.

----es me off that there is nobody on site with any ownership, or understanding of the buildings and their systems, there are two blocks approx 400 flats for christ sake.

I'm half tempted to just replace the controllers and note there may be underlying issues that need further investigations.

How would you guys approach this?
 
Don't think it's been asked, but did all eleven flats loose their timers at the same time, or was it cumulative over a period.
Following MJ’s theme - MOVs do degrade each time they react to over voltages. It is not unknown for them to eventually suffer thermal runaway which is when their quiescent current rises over time, the MOV warms up, its resistance reduces, it passes more current, it warms up even more…until it cannot dissipate the heat quickly enough to its surroundings and it destructs. All of which can happen in the absence of any overvoltage.
 
Don't think it's been asked, but did all eleven flats loose their timers at the same time, or was it cumulative over a period.
That is a good question but impossible to get a definitive answer as we don't know when they "went" only when the tenant discovered and reported them.

The first was reported on Tuesday, I was called on Thursday and by then there were eleven.

All we've got is the times they were reported.

But judging by the crazy disco lights I witnessed the issue is still ongoing and more will go.
 
@marconi I'll let you off if you can find a SIL through-hole bridge rec in a white package made in the last 25 years.?

We can now confirm from the PCB pics that the failed part is across the mains input. In theory it could have been a small filter capacitor but:
a) The part shape and burst pattern are more consistent with an MOV
b) A cap of those dimensions would typically be a Y-class part of a few nF which is not appropriate there.
c) An MOV is not a bad idea where a capacitive dropper is tapped off the supply to a relay-switched 16A load of unspecified characteristics.

What it will hopefully have been doing, before it popped, was shaving off transients likely to damage the dielectric of the X2 dropper cap, that would otherwise cause a progressive loss of capacitance to the self-healing process.

But judging by the crazy disco lights I witnessed the issue is still ongoing and more will go.

Somebody needs to switch this lot off now.
 
Just curious if you did any more voltage checks when you went back although I think to catch any major voltage peaks or dips you would probably need to put some logging equipment in across all three phases


Had a similar problem to this at a business premises I used to work from many years ago although no equipment was damaged the voltage would very often dip to 170 - 185v on one phase around 8:15 - 9:00 in a morning and around 17:30 - 18:30 in an evening but not everyday, after a few weeks we got the DNO involved who put a voltage logger in for a week who told us there was no problem found, a week later 4 DNO vans appeared one afternoon and dug up the link box at the end of the street about 50m away, talking to the DNO lads they said that the box was close to failing due to thermal damage and was being replaced with a resin joint, The voltage problem disappeared after that
 
They are rated at 16A. The hot water cylinders are on a dedicated circuit off their own 16A MCB, isolated via a 20A double pole switch, length is a couple of meters.

Couldn't see a rating on the element but looking into that now.

Edit to add,

The elements are 3kW but looking at the plumbing I think they're on a central hot water system as there seems to be a coil on the cylinders.

I'm back there tonight two replace a couple and grab some more info.
Time to get the Megger out and 1000v dc @ the heater could be cable or heater.
 
There's some really clever people on this forum. I had to Google the electronic references, and, after reading them for a few minutes, I realised I was mentally debating tea or coffee to start the day (I went for tea).

So I can't help you there. But I will try to using my old favourite, Ockhams Razor ie go for the bleeding obvious.

Lights flickering, different flats affected, electronic gizmos feeling unwell (my knowledge of such things shines). And all about the same time.

It stinks of a neutral connection. It's the only common denominator. I can't see 11 Sangamo clocks packing up at the same time (Greenbrook, maybe..)

I was (un)lucky enough to see a neutral on a three phase supply go AWAL first hand ('tis a long story) and it is frightening. Voltage between phase and (apparent) neutral 270. Nope, 370. Nope 300. Nope 280 etc. Modular fittings jumping up in the suspended ceiling. Vending machines dying in agony.

Ok, this was for a period of minutes. Bit it's proof that the voltage goes crazy with a naughty neutral. It may be the case that your neutral was just a bit cheeky and went missing for a second or so.

One to watch out for.
 
There's some really clever people on this forum. I had to Google the electronic references, and, after reading them for a few minutes, I realised I was mentally debating tea or coffee to start the day (I went for tea).

So I can't help you there. But I will try to using my old favourite, Ockhams Razor ie go for the bleeding obvious.

Lights flickering, different flats affected, electronic gizmos feeling unwell (my knowledge of such things shines). And all about the same time.

It stinks of a neutral connection. It's the only common denominator. I can't see 11 Sangamo clocks packing up at the same time (Greenbrook, maybe..)

I was (un)lucky enough to see a neutral on a three phase supply go AWAL first hand ('tis a long story) and it is frightening. Voltage between phase and (apparent) neutral 270. Nope, 370. Nope 300. Nope 280 etc. Modular fittings jumping up in the suspended ceiling. Vending machines dying in agony.

Ok, this was for a period of minutes. Bit it's proof that the voltage goes crazy with a naughty neutral. It may be the case that your neutral was just a bit cheeky and went missing for a second or so.

One to watch out for.
Have never seen that happen, don't know what supply type is being used over here we use TT
There's some really clever people on this forum. I had to Google the electronic references, and, after reading them for a few minutes, I realised I was mentally debating tea or coffee to start the day (I went for tea).

So I can't help you there. But I will try to using my old favourite, Ockhams Razor ie go for the bleeding obvious.

Lights flickering, different flats affected, electronic gizmos feeling unwell (my knowledge of such things shines). And all about the same time.

It stinks of a neutral connection. It's the only common denominator. I can't see 11 Sangamo clocks packing up at the same time (Greenbrook, maybe..)

I was (un)lucky enough to see a neutral on a three phase supply go AWAL first hand ('tis a long story) and it is frightening. Voltage between phase and (apparent) neutral 270. Nope, 370. Nope 300. Nope 280 etc. Modular fittings jumping up in the suspended ceiling. Vending machines dying in agony.

Ok, this was for a period of minutes. Bit it's proof that the voltage goes crazy with a naughty neutral. It may be the case that your neutral was just a bit cheeky and went missing for a second or so.

One to watch out for.
Must say that have never seen that happen, the reason that said about the Megger i
 
Have never seen that happen, don't know what supply type is being used over here we use TT
The TT or TN supply type won't make any difference to equipment damage if you have an neutral fault on a 3-phase group of circuits. What is more likely to make a difference to the stats is the types of cable/joints used that might alter just how common such a fault is.

Oh and the number of scroats stealing neutral links from sub-stations...

However at least with TT you don't have the open PEN risk for TN-C-S elevating external metalwork to tens or hundreds of volts...
 
Final update.

First thing, we have plague in the house so this may be my last post. We have one positive test and I'm fairly sure I've got it now, did my test this morning.

Interestingly my missus who, is a double jabbed devotee, is in bed (three days now) with it after catching it on a camping trip.

What exactly does this vaccine do?

-*-

Anyway had a chat with the contact at the flats this morning and to be honest I'm befuddled by her explanation.

They have had the situation looked at and resolved. Apparently it was "some flat plugging in too many appliances and burnt out a fuse and some wires"

I find this highly implausible.

Any overload should have been dealt with by the OCPDs in the flats and not downstream. Unless the design of the installation was seriously FUBAR.

More likely they got the installers back in to check it over and they've tightened up their loose neutrals.
 
Final update.

First thing, we have plague in the house so this may be my last post. We have one positive test and I'm fairly sure I've got it now, did my test this morning.

Interestingly my missus who, is a double jabbed devotee, is in bed (three days now) with it after catching it on a camping trip.

What exactly does this vaccine do?

-*-

Anyway had a chat with the contact at the flats this morning and to be honest I'm befuddled by her explanation.

They have had the situation looked at and resolved. Apparently it was "some flat plugging in too many appliances and burnt out a fuse and some wires"

I find this highly implausible.

Any overload should have been dealt with by the OCPDs in the flats and not downstream. Unless the design of the installation was seriously FUBAR.

More likely they got the installers back in to check it over and they've tightened up their loose neutrals.

Thanks for the update.

Hope the Covid doesn't get you too bad. I know some people who were affected for months.

Don't forget the vaccine is not 100% effective - no vaccine is.
 
Double vaccinated before I went to France three week ago, impossible to get a PCR test before I left my area, six different test laboratories refused to give me a test without an appointment, not much good as they only had appointments two weeks hence, went into Calais and had a test while I waited, all of this took hours, my normal six hour journey turned into thirteen and a half hours, the rules at Calais are very strict on the tests, at the UK side they did not want to see any documentation, just my passport, seems the French side is more strict than the UK side, hence letting all those FIFA people in without any checks, seems to be daft to me.
 
Final update.

First thing, we have plague in the house so this may be my last post. We have one positive test and I'm fairly sure I've got it now, did my test this morning.

Interestingly my missus who, is a double jabbed devotee, is in bed (three days now) with it after catching it on a camping trip.

What exactly does this vaccine do?

-*-

Anyway had a chat with the contact at the flats this morning and to be honest I'm befuddled by her explanation.

They have had the situation looked at and resolved. Apparently it was "some flat plugging in too many appliances and burnt out a fuse and some wires"

I find this highly implausible.

Any overload should have been dealt with by the OCPDs in the flats and not downstream. Unless the design of the installation was seriously FUBAR.

More likely they got the installers back in to check it over and they've tightened up their loose neutrals.
SKunk farm ? Anyway , i would like to know how their explanation would cause this issue (From a learning perspective )
 
Little of it makes any sense.

Don't get me wrong; I've been exceptionally careful with both sets of parents over the last 18 months, but none of the advice ever stacks up and I'm fed up with media reporting incomparable statistics - I'm not sure if this is a simple case of sensationalism or a deliberate intent to mislead.
 
"some flat plugging in too many appliances and burnt out a fuse and some wires"

I find this highly implausible.

I find it total BS.

As you suggest, the contractor might have fixed the problem but given the management office a waffly explanation to deflect blame. Or Chinese whispers; their guys gave an explanation that made sense but after a couple of re-tellings by non-technical people it's lost all meaning.

Anyway get well soon or better still hope you have't got it.
 
We had a broken neutral on our old house a few years ago, that was supplied (with our neighbours) via mural wiring on the back of the houses. The N connection between the houses was good, but intermittently high resistance to the supply N. The voltage went up, or down, depending on the loads on each phase (each house). When the lights got scarily bright, I put on the kettle.


In the 40 second video, the voltage doesn't go above 240V... but trust me, it did.

WPD ended up replacing about 10-20 items of blown electronic items in each of the 3 houses affected.

Luckily nothing burnt down.

Thanks for the original post, and all the contributions, interesting read. Get well soon.
 
We had a broken neutral on our old house a few years ago, that was supplied (with our neighbours) via mural wiring on the back of the houses. The N connection between the houses was good, but intermittently high resistance to the supply N. The voltage went up, or down, depending on the loads on each phase (each house). When the lights got scarily bright, I put on the kettle.


In the 40 second video, the voltage doesn't go above 240V... but trust me, it did.

WPD ended up replacing about 10-20 items of blown electronic items in each of the 3 houses affected.

Luckily nothing burnt down.

Thanks for the original post, and all the contributions, interesting read. Get well soon.

Any events like that lightning brownouts overvoltage

I usually knock off the RCD or the entire installation
 
If the supply goes I'd rather switch off as until fully restored as the supply can bounce on and off

Maybe leave a light switched on as an indicator

Wouldn't trust it not to damage the electronic equipment in my place
 
Final update.

First thing, we have plague in the house so this may be my last post. We have one positive test and I'm fairly sure I've got it now, did my test this morning.

Interestingly my missus who, is a double jabbed devotee, is in bed (three days now) with it after catching it on a camping trip.

What exactly does this vaccine do?
I think it is very difficult to actually identify how or where the virus was caught without there being any doubt especially when some people carry it without any symptoms and others can carry it for weeks before any symptoms show

But I do hope you all get better soon having had it twice I do feel for you as it can really knock you for more than 6 or at least it feels that way
Anyway had a chat with the contact at the flats this morning and to be honest I'm befuddled by her explanation.

They have had the situation looked at and resolved. Apparently it was "some flat plugging in too many appliances and burnt out a fuse and some wires"

I find this highly implausible.

Any overload should have been dealt with by the OCPDs in the flats and not downstream. Unless the design of the installation was seriously FUBAR.

More likely they got the installers back in to check it over and they've tightened up their loose neutrals.
I have never heard so much BS tosh

So who picks up the tab for the replacement timers
 
The tennants all made the same complaints of flickering lights and one long recent power outage.
Best guess, loss of neutral
Does sound suspiciously like that doesn't it.
It just baffles me that these building, under the management of a bunch of kids more interested in filling "units" than the safety of the tenants, are expected to manage themselves and you as a tradesperson should just be able to come in and "fix it".

Does anybody there even have the knowledge to comprehend that the have a potentially dangerous situation?
Well a building that size must have a formal management system in place - and no, it's not acceptable if the "kids" are having to manage this on their own. The management function needs to have - either in house or brought in as required - considerable specialist knowledge.
You might ask who the "responsible person" is and how to contact them directly.
Twice I have told them it needs attention, verbally and in writing via the job card.

I will chase it up on Monday as the lass who I was dealing with didn't convince me she understood the potential gravity of the situation.
I can think of a good way to get their attention. Big block of flats you say ? Just casually mention something like "you remember that tower block in London, Grenfell Tower ? Are you sure of all the fire safety in this building because there is potentially an electrical fault that could set light it up - and you could be in the dock to demonstrate why you aren't responsible for the ensuing deaths".
OK, a bit sensationalist - but if you're dealing with someone who doesn't want to hear any bad news, suggesting that they could find themselves in court on manslaughter charges is likely to wake them up.
I find it total BS.
Indeed. The only way I could see for tenants to cause any problem would be to load up the system with complex loads till the harmonics burn out the neutral. But that would a) be quite noticeable, and b) quite improbable.
As you suggest, the contractor might have fixed the problem but given the management office a waffly explanation to deflect blame. Or Chinese whispers; their guys gave an explanation that made sense but after a couple of re-tellings by non-technical people it's lost all meaning.
Either could be possible. I know from communications from my agent (I only use them for the initial let, but they still pester me over stuck that's none of their business) it's clear that they know nowt about electrics and can only regurgitate what's fed to them by "the trade" - i.e. the misleading lack of lies the scams have been putting out about EICRs over the last year or so.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Block of 200+ flats, eleven single channel hot water timers blown this week alone.