If you are referring to page 6 then you have ignored some of the advice and seriously misunderstood the rest.
 
Firstly - misunderstanding page 6 does not apply as that is not what was being referred to.

And I owe the OP an apology as, rereading, he seems to disagree with the advice on page 9 as well.

It is very poor advice as is usual in these guides.
What difference does IR >1MΩ make to the danger of unearthed exposed-conductive-parts.

In any case fitting a new CU will make the installation safer either way.
 
What difference does IR >1MΩ make to the danger of unearthed exposed-conductive-parts.

It's obviously to unsure there's no fault on the light fitting at the time of testing and no chance of an earth path if any future fault developed

I think this deals with real world
Situations quite well actually and is a pretty sensible guide

In practice you would obviously try to earth all fittings or replace with class 2 but as I last resort I think this is acceptable

As said before the installation would be a damn sight safer with a new cu rcds and main bonding rather than an old wylex

I still don't understand how I have seriously misunderstood this guide??
 