Search the forum,
Discuss Bonding of machinery control panels in the Electricians' Talk | All Countries area at ElectriciansForums.net
dasrik
Hi Guys,
I work for a large food factory, a couple of days ago a chap was electrocuted from a machine that had a bonding issue. Now we are being asked to check all the bonding on our machines.
But before i do i want to be sure what the requirements are, so far what i have found on machinery is pretty vague.
On the majority of our panels the incoming supply goes to an isolator and the earth is made off there and then taken to a bonding terminal or din rail earth connector. Is this ok or should the earth go to a MET first?.
The accident was caused by an earth coming off the din rail and not being connected to the MET a fault occured and the panel became live.
I want to find out what the right way is and what regs cover it if possible.
Cheers
are these panels supplied by SWA? if so, the SWA should be glanded to the metalwork of the cabinet,
No they are plug and socket 3 phase and single phase 16/32/64A depending on machine.
Sorry should of mentioned that before.
The DIN mounted terminals usually extend the earth onto the rail via the mechanical clamp which in turn is fixed to the chassis plate which is fixed to the enclosure. This earth path shouldn't be relied on as a safety earth. Where the earth is first made-off at the isolator it should be extended directly to the chassis of the enclosure and there should be a fly lead earth to the door as well. Also extended directly to the earth rings (banjos) of any glanding etc.
dasrik,
You are correct it is 60204-1, there are a few others, but, that is the most important.
You really need to understand the root cause here.
Also you should check the machine design drawings.
If you have had an electrocution on the premises then this is reportable under RIDDOR and you must not do anything until HSE & the Police have completed their investigation into the death.
Once you have their report then you should address this with the machine builder.
HSE will almost certainly request the technical file from the machine builder for proof of compliance with the machinery directive and the low voltage directives.
This is a very serious scenario and I strongly recommend that you get external professional support.
You may find that any actions you take could be found to be criminal until the investigation is completed as there could be charges of manslaughter brought.
Inteificio,
BS7671 GN's have no relevance to machinery, by the way it is GN8 that you are thinking of.
but does the OP mean electrocuted, or that the guy had a shock? big difference.
It wasn't fatal, but was a severe shock and is still in hospital with multiple fractures, it could of easily been a different story.
i'm sure the HSE will be involved. I haven't touched the machine although it has been modified - i refused to work on it and it is currently out of service.
There are no drawings for this piece of kit.
My original question is so i know how the machines should be wired to cover my own arse when fitting supply cables etc. We don't always have the luxury of wiring diagrams and the ones we do have might not cover the specifics of earthing arrangements.
I don't have access to BS 60204 although the company should have one.
The problem with working for large companies especially in the manufacturing industry, from what i have seen in my 12 years + we are pressured to keep lines going safety is often ignored by the people in charge and it is left to us who want to be sure we are doing the job right to try to find out the right way often in our own time and at our own expense. When things go wrong and there is an accident things change (sometimes) it shouldn't be this way but unfortunately in many factories it is.
Inteificio,
You must be minted then, because 7671 is one of the cheapest standards on a £ per page level & most people seem to moan about this.
60204-1 is currently £224.00.
The pdf is only 130 pages!
Check the value on 7671 now!
tel,
He has stated electrocuted, hence my post, there is a HUGE difference.
Correct terminology is quite important, I have been drumming this into my 2391 students today!
paul, that's why i raised the point. a lot of people will say electrocuted instead of " received a shock/belt". in either case H&S should be involved before it is a case of sudden death. obviously, if it were just a shock, then the investigation will not be as rigorous or as intensive as in a case of fatality, but either way, this could be a potential death trap and needs investigating and rectifying. any environment subject to vibration should have "belt &braces" terminations so that the failure of 1 connection doesn't lose the earthing from a metal fixture. ( this is also a good reason to fly lead the cpc to knock-out boxes ).
OK, dasrik in that case he was not electrocuted, else he would be dead, he suffered an electric shock.
As he has suffered fractures it is doubtful that it will not be reportable under RIDDOR, unless he has only got broken fingers, though as he has been hospitalised then it will almost certainly be reportable, and if he is off work for more than 3 days then it WILL be reportable.
I have a very good understanding of manufacturing and the line techs are to blame for most of the bad workmanship.
They must stand their ground and refuse to undertake unsafe work.
Thing is just like outside if one does this there will be another who will just do the mod/repair etc. and to hell with the consequences.
That is what is wrong, the ramifications are either misunderstood or they don't care.
You must remember that you are working under statute law.
This could open up a whole new can of worms.
This could well cost jobs or even the business once HSE get a hold.
Let me put it like this, IF I were the HSE inspector I would be pushing for a prosecution and a custodial sentence from somewhere.
If that were a line tech then so be it.
If that were the MD even better.
If you are working to a Std. then you must have access to that std. if you are modifying machinery then to comply with statute law you need to be working to 60204 thus you must be familiar with it and have access to it.
How are you complying with statute law if there are no machine drawings?
Is the machine CE marked?
What does your statutory PUWER98 assessment say about the machine control systems?
Don't tell me I can probably guess!
Your employer is probably an "almost" household name or at least well known in the business and their HSE "bods" are more interested in Hi-Vis, gloves & eye protection rather than fatal things like electricity, because like almost ALL HSE bods they have no real grasp of electrical safety.
tel,
You posted while I was typing.
This is a constant battle and it is almost lost due to the level of training of craftsmen, technicians and engineers we have in the UK at the moment.
Also you have the "little dictators" who wear the HSE hat who have little grasp of electrical issues.
As you say with regard to vibration, any rotating machine & I mean ANY WILL vibrate end of.
It is just the level of vibration that will vary.
There are so many machines wired with say 6491x or SWA, which is not an acceptable solution for vibrating machinery unless correctly applied that this is unreal and could be a death trap.
Thing is the correct connection methods are not taught any more!
Apart from the fact 6491x is never suitable for machinery anyway!
you're bang on there, paul. most H&S jobsworths are more concerned with harrassing workers who don't wear a hard hat while on the bog than getting to grips with real safety issues. till something drastic occurs, then they run round with their clipboards like headless chickens.
Wasn't the term electrocuted brought in after the invention of the electric chair to describe execution by electricity? Off topic a good way I know guys, it just got me thinking.
Sorry for getting the terminology wrong, every day is a school day as they say!
I have to be careful what i say on a public forum so the specifics will be a bit vague.
Paul you would be right when you say "almost household name" it will be reportable under RIDDOR and i am sure an investigation will ensue and hopefully it will lead to the company actually adopting a safer working practices model rather than just talking about it!
It is annoying that something like this has to happen before they listen or take any action.
The piece of equipment isn't CE marked and the panel was an "in house" creation by someone who is not competent and
i doubt has formal qualifications, but the company has thrown a multi-meter at him and now calls him an Electrical Engineer
which makes a mockery of the years college and apprenticeship the rest of us have completed. All of the other engineers
are unhappy that this person is allowed to operate in an unsafe manor and it has been brought up before on several occasions
yet nothing is done!
As i mentioned before we have no access to 602040 - are there any courses on these regs like there are for the regs?
What ever the outcome it still should be reported under RIDDOR for those who don't know what in means
Reporting of Injuries, Diseases and Dangerous Occurrences
which from the title the later applies if he has had an electric shock.
dasrik,
There are not many courses on 60204, you may find related courses at private training providers & equipment manufacturers.
I would not mind betting that I have been in one of your companies plants at one time or another.
There are sections of statute law with regard to competence, and selection of competent contractors, along with criminal and case law to back these up.
If I were your employers H&S advisor, I would be thinking about putting a case together to defend a HSE prosecution, because that is where this should be going IMHO.
I’ve been forced in to control modifications I didn’t agree with. But look at it this way, “make the changes or find a new job”, what do you do?
I came close to killing 4 people before I got the veto on control modifications that I felt would be unsafe.
Management hold the whip hand, production is everything! Safety? What’s that?
. "I haven't touched the machine although it has been modified"
Hi Dasrik: Just wondering, do you mean modified before the accident or since ?
Nice call Specialist!
If the machine has been changed since the accident and there is an investigation then it could mean a tempering with evidence case.
This would depend on the exact situation, how the IP was taken off site and several other small details.
Were the HSE & the Police informed immediately?
The severity of the injuries would dictate that, was the IP admitted via A&E, taken via ambulance etc.?
If they attended A&E then the hospital will inform the Police & HSE as a matter of course.
Hi Paul: I'm hoping Dasrik will come back & fill us in on the rest of the story, would also be nice to get an update on the Guy that got injured.
Unfortunately there seem to be a lot more Electrical "Accidents" in Industry than anyone ever gets to hear about or more to the point in a lot of cases nothing ever gets reported.
Inteificio,
I simplify things as on a forum. My statement should have read... I will pester the F$%^ out of the management until they buy me the dam PDF. =-)
Regarding value, however cheap bs7671 is, if it does not cover the standards I need then it is not good value.
I do like my BS7671, but am convinced that I am the only one who reads it sometimes. The amount of **** I get for expecting a circuit I am working on to be compliant is ridiculous. One of the supply circuits testing last week has a D63 breaker on it. To be compliant it wants a b40, I got shot down when I brought it up, so wrote out the maths clearly (needs to be in crayon for my manager to follow), still got shot down. He 'cites' experience is more important that correct rating.
Well due to pressure I signed off the circuit.... with his name ;-)
Specialist - The panel was modified after the accident (i don't know how much) but i'm pretty sure
it shoudn't of been touched at all, now the panel has been removed and the unit has been returned
to its original state which was pneumatic controls.
I don't know too much about the injury's the guy has but he is still in hospital and probably will be
for a while, with dislocations and fractures to at least one arm. Apparently he will need 2 operations to
re-set the dislocations. As far as im aware this was just from the shock!
i have been pestering for BS 60204 but still not seen it, i am now refusing to work on any panel until
i can be sure of the regs and have locked off a machine due to inadequate earthing. The annoying thing is
someone will probably of put it back in service over the weekend.
Ooh that stinks of cover up does'nt it ? Hope the Guy is going to be OK, was he working on a ladder or something when he got shocked ?
Just make sure to CYA by documenting everything you do & why you do it, if you lock off a machine then make sure you keep a note of it in a small notebook. It's too easy for Factory records to Dissapear.
Appologies if i'm preaching to the converted mate.
Specialist - The annoying thing is
Can't remember the exact rules on this, but I think it is your responsibility to make unsafe equipment unusable. Normally I would see it as isolate and lock off, or just cut the dam plug off if small equipment. However if you think your lock will be cut, and you consider it dangerous I would get creative.
A semi related example of being creative was our plug in 110v transformer (chained in) was being stolen repeatedly. Easy for an unskilled person to use a bolt cropper. So I got a 20kg transformer and wired it straight in to a 3 phase isolator. Most people would not know how to safely remove it from the isolator, and the weight will put people off too, so hopefully it will stay.
So if an unskilled person can remove the lock on an isolator, would they be able to identify a missing section of factory bus bar; or an introduced fault that will trip if the circuit is switched on?
If you think the machine is dangerous, make sure it cannot be used.
Specialist - i am enforcing a heavy amount of CYA! Especially as i am kicking up a bit of a fuss.
Inteificio - My issue with the machine is the specifics of the earthing, currently supply comes in to isolator but earth goes
straight to din rail, not the isolator earth terminal or the panel MET. As i don't know what the regs are on this and in order to cover my arse i can't do anything.
Next issue - lock offs, our procedure is... Lock off padlocks on a board in workshop if we lock a machine off we put the key back on the board so anyone can get access to. I'm pretty sure this isn't adequate.
Since the accident a rather hasty document has been put together that we have had to sign. It explains the importance of bonding panels and asks us to take all earths to the panel MET first, however without seeing the regs i don't think we can do anything to the earthing and may result in working machines being locked off - this will go down a treat :)
Does anyone with BS 60204 or access to it know if there are any specifics with regard to earthing and bonding inside?
Glad to see were on the same CYA page mate, Don't know off hand the Regs with regards to accessibility of Lock off keys but if I remember correctly they should only be accessible to Authorised persons. I worked in a Big Flour mill a while ago now & all lock offs were kept in a secure locked cabinet only accessible to us. When we wanted to do a lock off we took the kit, signed for it & then kept the key with us until the job was completed.
There are about 30 pages (ish) with regard to connections & earthing.
Also the equivalent to BS7671 Section 441 is referenced as being required along with 543 & 554 will look for a bit more later.
Cheers Paul,
I have had a look at the Regs and haven't found too much that helps. In my book 441 is "reserved for later use". I can't quite remember what the other ones said but one covered incoming earth - most of our machines are on a plug and socket so this is limited by the supply, i think?
FYI - the hospital are classing the injured guy as having been Electrocuted apparently they use this to class severe shocks where the person could quite easily of died.
Just thought i would add that in - i now feel vindicated in my use of terminology :)
I have another query but i will start another thread about that, this one is getting a bit long.
Reply to Bonding of machinery control panels in the Electricians' Talk | All Countries area at ElectriciansForums.net
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Hi guys I have a few questions regarding my findings today and wondering if any of you could help one of the guys asked me to have a look at an...
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
We're in the UK, 240v lighting feed. We have replaced all the lights in our house with LED ceiling panels. These are pretty much the standard...
Hi I work for a Manufacturing company based in Cheshire East, in our factory we have a 1940's era 10CWT Lift manufactured by Evans Lifts - which...