Is that one gas supply bonded? Are there no certs available.. i would hesitate to guess they have been bonded to MET but you should be able to locate them. Treat the sub as a circuit and carry on with your consumer unit change, if you want to bond in flat you may but isnt necessarily req so dont worry about the 6mm cpc supplying flat. What size fuse is in submain switch fuse,
 
All gas meters come from the same supply, each flat has own meter.

Surly these would be earthed by the DNO, I just can't find the DNO MET.
How do know the earthing system then, is there a Ryefield board that could have a combined neutral/earth bar.
 
Is that one gas supply bonded? Are there no certs available.. i would hesitate to guess they have been bonded to MET but you should be able to locate them. Treat the sub as a circuit and carry on with your consumer unit change, if you want to bond in flat you may but isnt necessarily req so dont worry about the 6mm cpc supplying flat. What size fuse is in submain switch fuse,

No certs available, I located the gas meter and this isn't bonded and neither is the gas/water pipping within the flag. There is a 60amp fuse in isolator for each flat in the DNO cupboard.

How do know the earthing system then, is there a Ryefield board that could have a combined neutral/earth bar.

Each flat has a 60amp isolator labeled PME. There is another cupboard which is expect has a Ryefield board inside but this is locked.

Thanks for everyone's help do far.
 
Just wondering if you carried out Ze, best do that 1st and take it from there.
I think you will find it will be within limits.

Ive seen loads of 6mm earths and tested fine and no you can not TT, if you have an issue with the earthing you ring dno.

Good luck
 
Just wondering if you carried out Ze, best do that 1st and take it from there.
I think you will find it will be within limits.

Ive seen loads of 6mm earths and tested fine and no you can not TT, if you have an issue with the earthing you ring dno.

Good luck


Double ehh????
 
Really ??? Where??

Cant see where im repeating you, do apologise if that has offended you and others.

Thank yu

Hi @Sparkie30 you havent offended anyone but your reply made little sense to the OP predicament..
1-how is checking ze going to help with his bonding predicament
2- the op hasnt questioned any ze max values
3- yes you can TT without contacting DNO
 
If the main earthing conductor is 6mm and has been in place for quite a few number of years and shows no signs of thermal damage it maybe adequate
By carrying out the aidiabatic equation it maybe an adequate CSA and can be left and a note made on the certificate
 
If the main earthing conductor is 6mm and has been in place for quite a few number of years and shows no signs of thermal damage it maybe adequate
By carrying out the aidiabatic equation it maybe an adequate CSA and can be left and a note made on the certificate

But the bonding issue?
 
If the main earthing conductor is 6mm and has been in place for quite a few number of years and shows no signs of thermal damage it maybe adequate
By carrying out the aidiabatic equation it maybe an adequate CSA and can be left and a note made on the certificate
It isn't the earthing conductor it is a cpc. The issue is its ability to support PME bonding.
 
Hi @Sparkie30 you havent offended anyone but your reply made little sense to the OP predicament..
1-how is checking ze going to help with his bonding predicament
2- the op hasnt questioned any ze max values
3- yes you can TT without contacting DNO

1- Ive never said checking ze is going to help with his bonding
The op was asking about his earthing in his 1st post
2- the op has said its pme so i guess he knows max ze value
3- no you cant unless you get permission from local authority and survey the area, and im sure if you have a eathing issue ukpn or local authority will attend pretty quickly from my experince anyway.
 