Discuss Changing consumer unit in flat in the UK Electrical Forum area at ElectriciansForums.net

Really ??? Where??

Cant see where im repeating you, do apologise if that has offended you and others.

Thank yu

Hi @Sparkie30 you havent offended anyone but your reply made little sense to the OP predicament..
1-how is checking ze going to help with his bonding predicament
2- the op hasnt questioned any ze max values
3- yes you can TT without contacting DNO
 
If the main earthing conductor is 6mm and has been in place for quite a few number of years and shows no signs of thermal damage it maybe adequate
By carrying out the aidiabatic equation it maybe an adequate CSA and can be left and a note made on the certificate
 
If the main earthing conductor is 6mm and has been in place for quite a few number of years and shows no signs of thermal damage it maybe adequate
By carrying out the aidiabatic equation it maybe an adequate CSA and can be left and a note made on the certificate

But the bonding issue?
 
If the main earthing conductor is 6mm and has been in place for quite a few number of years and shows no signs of thermal damage it maybe adequate
By carrying out the aidiabatic equation it maybe an adequate CSA and can be left and a note made on the certificate
It isn't the earthing conductor it is a cpc. The issue is its ability to support PME bonding.
 
Hi @Sparkie30 you havent offended anyone but your reply made little sense to the OP predicament..
1-how is checking ze going to help with his bonding predicament
2- the op hasnt questioned any ze max values
3- yes you can TT without contacting DNO

1- Ive never said checking ze is going to help with his bonding
The op was asking about his earthing in his 1st post
2- the op has said its pme so i guess he knows max ze value
3- no you cant unless you get permission from local authority and survey the area, and im sure if you have a eathing issue ukpn or local authority will attend pretty quickly from my experince anyway.
 

Reply to Changing consumer unit in flat in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
770
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock