chris06749

Will these be any issues running a Chinese 3 phase motor, 380v 50z motor on standard UK 3 phase mains?

Will be used for a few hours max each day

Are we likely to have over heating problems?

Would we be better off modifying the wiring/using a transformer of some kind? What are the likely costs involved?

As you can tell I know very very little about this so all help greatly appreciated!

Regards
 
Does the rating plate offer other voltages? Most motors can be configured 380/400/440v in either star or delta configuration. Are there removable links in the terminal chambe
 
Hi

appreciate the reply

the seller just told me that
' For power supply 3P 380V 50HZ, the motor can work in the range from 380-410V. And the terminal chamber are the same !'

would this be in range and suitable for uk 3 phase ?
 
Hi

appreciate the reply

the seller just told me that
' For power supply 3P 380V 50HZ, the motor can work in the range from 380-410V. And the terminal chamber are the same !'

would this be in range and suitable for uk 3 phase ?

Really???? What voltage would you like the motor to run at? I have lots more questions but im too grumpy today to type...
 
You’re supply will most likely be 433V. it’s up to you if you use it.

Probably be cheaper to change the motor and the control transformer.
 
Our MD loves to buy antique machines, we have a few machines rated at 380V all the way around, our supply varies from 415-440V. Never had any issues with this.
 
It will be absolutely fine. Cheap Chinese motor anyway!! Fully expendable lol

What's your voltage at the origin? Might be on the lower side of the nominal voltage anyway plus a bit of VD underload will bring it down a bit more.
What is the motor application? What size is it? Are you using a VFD?
 
Most motors rated at 380v 3-phase will run fine on a 440v 3-phase supply. There's a very small chance of overheating if the motor is running at more than than 90% of it's rated current. If it's running close to it's max current then prolonged minor overheating tends to cause premature bearing failure due to lubricant breakdown rather than winding damage so keep an eye on the bearings.
Also, obviously connect up the controls to include the thermal safety contact or NTC if the motor has one built into it.
 

Reply to Chinese 3 phase, 380v 50z motor on UK 3 phase mains in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
511
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
636
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
262
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock