why not fit a relay at the fire alarm panel end to do the switching of the C1 + C2 contacts and then use the 70m cable run to switch on the relay ??
 
thinking about this more...

you are extending contacts C1 and C2 to a switch 70 metres away that will short those contacts to set off the alarm....

surely that length of run is more than 70 metres as the current has to run down core 1 of the SWA to the switch at the end and then back down core 2 to the panel to complete the circuit ??

so surely your length is now double ?? so more like 140 metres ??

i might be totally wrong here lol
 
If it was pulsing that was needed, i was nearly going to suggest ( i have now) a indicator relay (like one that's used in a car, truck etc), powered/latched by the timer then it pulses to the c1 + c2 on the panel, then there would be issues with that complying to standards i think...
 
The length of pulse is for the duration of the bells sounding, in schools say you wish to have a 4 secound bell for class change, then using a normal digi timer will only switch at 1 minute intervals, so a normal timer will give you a 1 minute bell ring. Using pulse timer you can set out contacts for 1 sec interval...so setting for 4 seconds gives the required bell duration.
 
The length of pulse is for the duration of the bells sounding, in schools say you wish to have a 4 secound bell for class change, then using a normal digi timer will only switch at 1 minute intervals, so a normal timer will give you a 1 minute bell ring. Using pulse timer you can set out contacts for 1 sec interval...so setting for 4 seconds gives the required bell duration.

Ahh, i see. Its good to learn more, im only starting out
 
All here to learn off each other, thats what makes a good forum.
Throw it in....debate it....get the answer...!
 
thats the thing we still have not got an answer?!
what was the problem.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Class change on a Gent 4 zone fire alarm panel
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
42

Advert

Thread statistics

Created
markysparky108,
Last reply from
michaelw6,
Replies
42
Views
13,649

Advert

Back
Top