Snowhead: I agree that would seem logical. And I thought that for a while as well, however I cant square it with my observations. The total leakage of all annex connected equipment (excluding pump) is about 7mA. The leakage of the pump is zero (unless it is more at startup). The leakage of appliances on my ring main (where it works fine) I assume to be rather more than 7mA. *However - I will do this check to confirm*.
 
monkeyelectric: I have an AC ammeter which I can insert into the earth lead of an individual applicance. I also have a device which does a similar job to a ramp tester. (It is a decade resitance box. Just keep adding in 1mA until it trips).
 
Hi
Have you done any insulation resistance tests on the annex? Possibly N-E fault on a circuit, had this happen before and I know the these vsd's and rcds can be trouble some. If using a vsd with an rcd it should be of a b type really. Hope this is of use.
Regards
Gary
 
Thanks everybody for their help. I will go and do some more tests and repost the results in a few days. Hopefully they will show a smoking gun ... though I suspect not......
 
Tony: You may be right - but I've done that twice .. and paid for 2 x 1 days rate with no appreciable advantage. If possible I want to be able to present any electrician with the 'smoking gun' so that he can take remedial action.
 
Tony: You may be right - but I've done that twice .. and paid for 2 x 1 days rate with no appreciable advantage. If possible I want to be able to present any electrician with the 'smoking gun' so that he can take remedial action.
To be honest if they were decent electricians it should be them finding the problem not you! What exactly did they do to try and resolve your problem in that day they spent looking?
 

Reply to Complex motor start cuasing RCBO to trip problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a submersed bore pump 85M down and covered by 40M water. The motor/pump is 1.1HP, capacitor run, 35uF in a capacitor box above ground, with...
Replies
5
Views
3K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
21
Views
9K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock