This could be down to a loose connection to the annex but only shows under heavier loading or inductive loading hence your motor, get the electrician to check all consumer side connections are sound, try plugging an heavy load into the offending circuit and see if this too causes similar tripping to re-enforce the theory.... all bus-bar links etc need checking also DNO connections could be and issue too, making a temp set up of the tails to the annex using the rcbo that trips this will eliminate any issues within your fuse board but obviously a competent electrician needs to do this... there is another possible cause but il reserve bringing this up so not to over complicate things at the moment.