HI,

I have a difficult to diagnose problem. I've had two qualified electricians try and sort it, but no solution yet.
It is tricky (interesting?) and would love to hear comments/suggestions.

I have a long barn conversion.

Supply enters one end into a CU. There is a 50A 30mA RCBO feeding a 16mm T&E which goes about 50yds to an annex where it terminates in a standard split load CU. (Two 30mA RCDs with assorted MCBs each side).

Because the earth conductor in 16mmT&E is of insufficient size, an earth spike is additionally connected at the annex end.

One MCB supplies a 'pump room' which supplies a bore hole pump and - recently - a variable speed water pressure pump.

Every time the variable speed pump starts it blows the RCBO. (Never the RCD).

But, it is not faulty. If plugged into a regular socket on my main house ring main it works fine.

I have a socket near the main CU also connected to the RCBO - for test purposes.
If the pump is plugged in there it trips the RCBO ONLY IF the annex DB main switch is on, and at least some MCBs are enabled.

The situation is fully reproducible - although putting MCBs on in turn gives inconsistent results.

My personal view is that this is related to the earth spike having a substantially lower inductance to earth for the startup motor current and 30mA is current flowing through some domestic appliance in the annex to the spike. However, this is difficult to argue as the problem occurs when the pump is pugged in at either end of the 50yds 16mm cable.

Supply appears to be TN-C-S (although there are 3 cables coming from the transformer outside).

Any clever ideas?

Peter

PS All Zs etc within spec. 1V shown on test equip between N and E in whole installation!
 
Darkwood: Many thanks for the long explanation yesterday. I've now read it in detail. A couple of points:

1. FYI an adjacent property had a problem whereby use of a large flymo in house A cause RCD to trip in house B. (Mine is house C). A little like the scenario you mention.

2. You say (imply?) that there are clever RCBOs available which 'recognise' the inverter maveform and discount it. If so - please can you point me at a spec/partnumber etc?

3. Electrician coming next week - will do all the tests. Meanwhile I have just received a clamp meter and will do some more accurate measurements myself.

4. "Vetted". Well Chartered Engineer & elecSa approved is all I know.
Regarding your point 1 that's what I briefly suggested earlier regarding proximity of transformer but with your added info regarding neighbours then this is more than likely the cause... ive heard of this problem before with neighbouring properties creating nuisance tripping in a different building, its possibly caused by issues between the properties using a common transformer that's in close proximity the exact cause was never identified but because it may be a neighbouring installation or the DNO's issue it gets very hard to resolve.

Point 2- Schneider do an RCCB in their SI range that's designed to recognise the generated earth leakage from power drives, computers, electronic lighting etc ---product code 25524 - this is a 40amp double pole RCCB unit so it would be fitted in a separate enclosure and doesn't provide overload protection so you feed it from a standard mcb then connect load to outgoing side.

Point 4.... let him peruse this thread, its not common knowledge this issue your having so may head him in the right direction. Note this hopefully will eliminate the inverter causing tripping but may not stop the other nuisance tripping issues you had although it does filter stray frequencies and may stop the nuisance tripping caused due to neighbouring installations and proximity of transformer but I cant say if it will or not.
 
Last edited by a moderator:
Hi All,

well I did have an IR test scheduled but I have just cancelled it.

What I didn't mention was that the annex in question is rented out as a holiday home - and I really would prefer to not disturb them. I'll wait until november when we may have a spare week.

Also, I followed advice here and purchased some "proper" test equipment. Specifically a min/max clamp meter.

I discovered that the Variable speed pump has a max of 35mA at startup, and 20 thereafter. Not sure why my ammeter in the earth line didn't notice this, but there you go.

I have two solutions at the moment - both rubbish, but they work:

1. Connect the whole of the pump room to the other property - and show the problem doesnt recur .. thus blaming the pumps.

2. Replace the RCBO with an RCD and MCB. Logically equivalent, but I have experimental observations which says one blows and the other doesn't. [ I do notice the RCBO has an earth lead which according to literature enables it to 'blow faster'. ]

I still have a very funny earthing system.

There is one more thing I'd like advice with however:

With the new clamp meter I measured the current in the earth spike lead. Small 3mA. OK. But then I realised that my property and the property next door share a gas supply. The supply comes in copper into each property. In accordance with best practice installers have bonded these incoming copper pipes to the local earth.

To my mind this then creates more opportunity for ground loops etc etc. I measured the current in the gas bonding line. It was non-trivial. Varied but perhaps 10-20mA.

Any comments?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom