Well to be honest, that particular requirement seems to have been brought in as a knee jerk reaction.
No real thought has gone into it.
Should we allow a time limit, should there be a minimum temperature, should the item be designed to withstand fire only from within or also externally?
At present there is no requirement to retain any fire within the enclosure.
A whole raft of things which will need to be looked into.

A CU is a type tested DB and is used to distribut a supply into separate circuits.
Anything similar would have to do the same.
As such any device (such as an isolator, Henly block, switch fuse, up front RCD, etc.) which does not divide a supply into separate circuits would not be deemed similar.
However, a fire alarm panel could well be deemed as being similar.
 
A CU is a type tested DB and is used to distribut a supply into separate circuits.
Anything similar would have to do the same.
As such any device (such as an isolator, Henly block, switch fuse, up front RCD, etc.) which does not divide a supply into separate circuits would not be deemed similar.
However, a fire alarm panel could well be deemed as being similar.

Thanks for the reply. Have you a source or citation on those statements? And I'm not backing you into a corner, I would love some clarification on these matters.
 
Lol no not really.
Unfortunately the definitions in BS7671 are not very good.
For instance the definition of DB could describe a switch fuse, FCU or even a 13A plug. The definition of a circuit could describe a washing machine or fridge freezer.
However Regulation 133.1.1 requires:
"Every item of equipment shall comply with the appropriate British or Harmonized Standard. In the absence of such a standard, reference shall be made to the appropriate International (IEC) standard or the appropriate standard of another country."
The fact that DBs, CUs or the new description for CUs DBOs (DBs intended for use by Ordinary persons) are required to comply with a different set of standards (BS EN 60439 replaced by BS EN 61439), to the standards which isolators, Henly blocks and switch fuses are required to comply with (BS EN 60947), would to my mind suggest that at least as far as BS EN Standards are concerned, they are not similar.
 