I am fitting a new dual CU that comes with 10MCBs. For those that are unused is it acceptable to just leave them installed but switched off and identified as unused. Or should they be removed and replaced with blanks?
Discuss Consumer Unused Spare ways in the UK Electrical Forum area at ElectriciansForums.net
i keep them installed, as the customers usually like the idea that they have got spare breakers.
and for my sins i keep them switched on, customers usualy only need to access the board to re-set a trip, if spare breakers are down aswell can confuse the clueless.
im sure that iff they are installed correctly then theres no issues, may be wrong
i leave them in, simply because it's all too easy for those stupid clip in blanks to fall out and compromise the IP rating, leaving a hole just right for a child's fingers to poke in and touch the live busbar.
i totally agree, but most CUs come with the clip in ones or none at all. as malc. says, if the customer has paid for a fully loaded board then he gets a fully loaded board.Tel the only place for clip in blanks is the bin they should be banned I fit din mounted always they cant fall out.
J
Surely if your fitting a new board adjacent to it will be a circuit identification chart as required by the regulation 514.9.1 in the big green book ? So users of the installation are aware of points of utilization etc
ATB J
Surely if your fitting a new board adjacent to it will be a circuit identification chart as required by the regulation 514.9.1 in the big green book ? So users of the installation are aware of points of utilization etc
ATB J
i leave them in, simply because it's all too easy for those stupid clip in blanks to fall out and compromise the IP rating, leaving a hole just right for a child's fingers to poke in and touch the live busbar.
Lucky to find a new CU labelled round here let alone a circuit charge
Surely if your fitting a new board adjacent to it will be a circuit identification chart as required by the regulation 514.9.1 in the big green book ? So users of the installation are aware of points of utilization etc
ATB J
Yes of course. Not really sure what this has got to do with the thread though.