The first house I bought had a clock point on the dining room wall.

I only found it when I was striping the wallpaper to redecorate.

Then I found out it was wired with some stuff that looked more suited to wire a door bell running diagonally down the wall onto the back of a double socket and covered with the thinnest skim of Polyfilla I've ever seen.

All it needed was for some wifey to stick a calendar in the "wrong" place with her drawing pin and there could have been a right bonny gan on.

where did you but your polyfilla from?
 
Hmmmm I see what you mean 10mm would be to big.
If they never fitted 10mm I would probably be ok.

There needs to be separate iso switches because the appliances are over 2m apart.

Ok, whats best then? If they were fitting electrical appliances they most likely would have been wired directly and not a problem but as they most likely will just have 13A plugs what should I use?

I'm assuming that the gas appliances are not supplied with plugs, if they are I was thinking a socket would be OK to fit at the ends of the cooker cables. If in the future the appliances are changed to electric the sockets can be removed.
 
There needs to be separate iso switches because the appliances are over 2m apart.

What matters is not how far apart the two appliances are, but how far away from the switch they are. What's more, I don't believe that the requirement for an isolator within 2m of the appliance is contained in either the building regs or BS 7671, just in the Electrician's Guide to the Building Regs. So, provided that both the appliances are in the same room, I think that a single isolator would be a reasonable compromise, particularly if it's properly labelled.
 
What matters is not how far apart the two appliances are, but how far away from the switch they are. What's more, I don't believe that the requirement for an isolator within 2m of the appliance is contained in either the building regs or BS 7671, just in the Electrician's Guide to the Building Regs. So, provided that both the appliances are in the same room, I think that a single isolator would be a reasonable compromise, particularly if it's properly labelled.
Well maybe, but he has stated that they will be on opposite sides of the kitchen and then there's the "small" matter of running the cable!!
 
Sorry I should have said, the appliances will be over 2m apart and as the original iso switch is on the over side of the kitchen, it will also be over 2m away from the new hob location.
 
Well maybe, but he has stated that they will be on opposite sides of the kitchen and then there's the "small" matter of running the cable!!

Unless the kitchen's huge, I would worry about it.

As for the small matter of running the cable, he might be lucky and have a suspended floor. :smile5:
 
You won't get a 10mm in socket outlet terminations

You can....I'm bored so to test your claim I went and got a piece of 10mm2 cable scrap, stripped it and terminated it into an MK double socket (likely would also work with a single) I have in the stock box...it fits...just...and screws down securely.
Would definetely need a 47mm deep back box though....
 