2wireit
6mm to kitchen.
Separate hob and oven. Rating combined just under 13000w
Am I right in applying diversity and the two appliances sharing the same supply.
45a dp switch off to two ccu's
32amp mcb 60898
6mm supply cable
T.i.a
6mm to kitchen.
32amp mcb 60898
6mm supply cable
T.i.a
Are you a real electrician?
Pete do you have any positive input? I far from know everything. Thought you could ask advise on here ??
Got no books to hand I'm away. Job is am tomorrow. So thought I'd ask as not done domestic in a while. Advise would be great as to confirm this is ok. I remember reading up about diversity for cooker supplies. Thanks. Don't be to hard on me please
32A MCB to 6mm T/E ( assuming not run through a load of itchy-poo) to 45A isolator to dual (or 2 separate) CCU, 1 to hob, 1 to oven job done get paid ..next.
What about the case where the oven comes with a 13amp plug on the end?
Chop the plug off and proceed as normal, a 13A plug on a fixed appliance not subject to overload is just an unnecessary potential point of failure.
Job done. thank you for advice telectrix. combined load was actually 10.10kw. upon install.
hob 5700kw
and oven 4400kw.
just thought id leave feedback !
hob 5700kw
and oven 4400kw.
yhat adds up to 10,100kW. you'd need Wylfa Nuclear Power Station to run that.