Discuss Cooker - diversity. A second opinion would be nice in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Are you a real electrician?6mm to kitchen.
Separate hob and oven. Rating combined just under 13000w
Am I right in applying diversity and the two appliances sharing the same supply.
45a dp switch off to two ccu's
32amp mcb 60898
6mm supply cable
T.i.a
Pete do you have any positive input? I far from know everything. Thought you could ask advise on here ??
if you are a spark ,then you should not be asking that question!Pete do you have any positive input? I far from know everything. Thought you could ask advise on here ??
What about the case where the oven comes with a 13amp plug on the end?32A MCB to 6mm T/E ( assuming not run through a load of itchy-poo) to 45A isolator to dual (or 2 separate) CCU, 1 to hob, 1 to oven job done get paid ..next.
What about the case where the oven comes with a 13amp plug on the end?
yhat adds up to 10,100kW. you'd need Wylfa Nuclear Power Station to run that.Job done. thank you for advice telectrix. combined load was actually 10.10kw. upon install.
hob 5700kw
and oven 4400kw.
just thought id leave feedback !
Now ahaalmost gave you a disagree there. how can there ever be too many beers?