Hi all,

I have an engineer who has failed a wall mounted data cabinet because the PDU is hard wired into a switched fused spur, the spur is spurred off a ring main in 2.5/1.5 twin and earth.

He has failed it under regulation: 543.7.203 The wiring of every final circuit and distribution circuit intended to supply one or more items of equipment, such that the total protective conductor current is likely to exceed 10 mA, shall have a high integrity protective connection complying with one or more of the following:
(ii) A single copper protective conductor having a cross -sectional area of not less than 4mm, complying with the requirements of regulation 543.2 and 543.3, the protective conductor being enclosed to provide additional protection against mechanical damage, for example, within a flexible conduit.

My question is, how can you determine the protective conductor current of a piece of equipment? This is a wall mounted cabinet with a few switches in it, no servers pulling high amounts of power and I doubt the cabinet as a whole is exceeding 3.5 mA (Reg 543.7.201) let a lone 10 mA. Unfortunately I am not signing my name to the test results and I need to make sure we're doing things properly.
 
Hi all,

I have an engineer who has failed a wall mounted data cabinet because the PDU is hard wired into a switched fused spur, the spur is spurred off a ring main in 2.5/1.5 twin and earth.

He has failed it under regulation: 543.7.203 The wiring of every final circuit and distribution circuit intended to supply one or more items of equipment, such that the total protective conductor current is likely to exceed 10 mA, shall have a high integrity protective connection complying with one or more of the following:
(ii) A single copper protective conductor having a cross -sectional area of not less than 4mm, complying with the requirements of regulation 543.2 and 543.3, the protective conductor being enclosed to provide additional protection against mechanical damage, for example, within a flexible conduit.

My question is, how can you determine the protective conductor current of a piece of equipment? This is a wall mounted cabinet with a few switches in it, no servers pulling high amounts of power and I doubt the cabinet as a whole is exceeding 3.5 mA (Reg 543.7.201) let a lone 10 mA. Unfortunately I am not signing my name to the test results and I need to make sure we're doing things properly.
You need an Earth Leakage Clamp Ammeter, (not a cheap item)
 
Have they quoted what the protective conductor current was?
 
Hi all,

I have an engineer who has failed a wall mounted data cabinet because the PDU is hard wired into a switched fused spur, the spur is spurred off a ring main in 2.5/1.5 twin and earth.

He has failed it under regulation: 543.7.203 The wiring of every final circuit and distribution circuit intended to supply one or more items of equipment, such that the total protective conductor current is likely to exceed 10 mA, shall have a high integrity protective connection complying with one or more of the following:
(ii) A single copper protective conductor having a cross -sectional area of not less than 4mm, complying with the requirements of regulation 543.2 and 543.3, the protective conductor being enclosed to provide additional protection against mechanical damage, for example, within a flexible conduit.

My question is, how can you determine the protective conductor current of a piece of equipment? This is a wall mounted cabinet with a few switches in it, no servers pulling high amounts of power and I doubt the cabinet as a whole is exceeding 3.5 mA (Reg 543.7.201) let a lone 10 mA. Unfortunately I am not signing my name to the test results and I need to make sure we're doing things properly.
Ben does the item of equipment have an details as to the predicted earth leakage? I take it from your post that the Ring Final Circuit RFC has not been wired as per regulation 543.7.2.201 pagev87 On Site Guide 18th Edition
 
Thank you for the replies, I misunderstood the whole picture of the failure and focused solely on this problem, I am human and still learning the vast information the BS hold! Next question is how do I remove a post so I don't get bombarded with replies?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Warminster
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Norbeck

Thread Information

Title
Defining what equipment has protective conductor current
Prefix
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
Ben Murray,
Last reply from
westward10,
Replies
10
Views
4,228

Advert

Back
Top