When wiring a domestic kitchen is ok to supply integrated appliances from 32A/ 2.5mm ring via 20A D.P. Multi grid Switches , using 2.5mm on out going side of switches to a 1 gang socket or spur ?
 
Some appliance manufacturers specify a 16a over current device. So if you are strictly following the M.I then putting the appliance directly on a 32a ring is not correct.
of course the appliance will work hardwired directly to the 32a ring and I have done this on occasion but technically it’s not correct unless fuses down to the correct rating
 
A grid switch set up is totally compliant. It’s just spurs off an rfc.... although branched off very close together within the same box.
As with any infused spur, you can feed a double socket... but not usually done in a kitchen environment... single sockets only.


The above is for a “standard” rfc 32A OCPD
 
That’s how a lot of new builds are done. Although I think there’s a few on here who don’t like using 20A DP switches protected by a 32A ocpd.
Never understood that myself as a standard domestic appliance would never draw anywhere near 20 amps. I think they assume that the DP switch would have 32 amps flowing through it rather than just the supply side terminations taking the current.
 
20 amp DP switches are used on the grid for isolation/maintenance purposes only, nothing to do with having only 20 amps max through the switch or whatever as installing a fuse or a fused connection unit would be pointless considering the appliance plug has a fuse inside it.
 
Some appliance manufacturers specify a 16a over current device. So if you are strictly following the M.I then putting the appliance directly on a 32a ring is not correct.
of course the appliance will work hardwired directly to the 32a ring and I have done this on occasion but technically it’s not correct unless fuses down to the correct rating
The plug has a 13 amp fuse in it so that’s not technically accurate, more like the instructions cater for the European 16amp socket arrangement where there is no fuse inside a plug.
 
20 amp DP switches are used on the grid for isolation/maintenance purposes only, nothing to do with having only 20 amps max through the switch or whatever as installing a fuse or a fused connection unit would be pointless considering the appliance plug has a fuse inside it.
The grid switches in many of the late 2000s new build flats I've been in recently all have fusing at the grid switch - but I think when new they had appliance outlet plates at the appliance so no fused plug.

That may have been to avoid having to put them on the RCD side in the CU, or because they thought it was neater - but most have since been replaced with single sockets since they're almost all rented and tenants prefer to plug a fridge in....
 
Last edited:
Out of interest, in what circumstance would you not need to use 2.5mm on the outgoing side?
When the cable is

a) Adequately protected from overload by a downstream device and/or the nature of the load. ✔️
b) Adequately protected from faults by the upstream device. ✔️



And even if you didn't need to, why wouldn't you?
To avoid waste, and have an efficient design.

Looked at the other way, why would you use an oversized cable?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Domestic kitchens
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
16
Unsolved
--

Thread Tags

Tags Tags
domestic

Advert

Thread statistics

Created
Toshie,
Last reply from
Soi disant,
Replies
16
Views
2,860

Advert

Back
Top