H
hutch6447
Hi all ran supply to outdoor garage as this is being assessed just want to double check.
Main consumer Board 32 amp RCBO ran on 4mm SWA to the garage then onto the garage consumer unit.
Ran overhead but less then 3 metres length between house and entry point at garage, so just ran it direct.
Running into the garage consumer got the SWA on a banjo connection then going on to power the 30mA rcd.
MCB's in garage are 1 x 20A 1 x 6A
Plug sockets Radial ran on 2.5/1.5
Lights ran on Radial 1.5/1.0
Ran all test's and they were well inside limits BS 7671
and cable support. catenary?
What's the earthing system at the origin?
If you have an RCD at the garage end, you won't have discrimination between that and the RCBO. Do you need an RCBO (because of cable installation method)? Can you replace it with an MCB?
As mharries says, what height? How have you supported this cable?
The final circuits in the garage sound OK.
Less than 3m span so therefore no additional support required. What is the height of the cable? I'm assuming you supplied it via an RCBO because you have no RCD in the main CU and wanted to protect the cable?
Yes height of cable is 3.5m high, and the span across from house to garage is less than 3m so i have not put supports on. Got it on RCD IN GARAGE and 20A mcb and 6A mcb sockets/lights but the main run back to the main consumer board i have put on a 32A rcbo.
As said above, no discrimination between the RCD in the garage and the RCBO in the main consumer unit. I'm no expert but I wouldn't have thought the SWA feeding the garage needed RCBO protection?? Daz
ditch the RCBO at the house and use a MCB. or use a time delay RCBO --££££££s
Yeah I understand no discrimination but meeting requirements of 17th edition split boards will be rcd protected on one side and the main switch side either on rcbo's or another rcd so for sake of the assessment it will just having double protection on the rcd side, and i have 32 A protection on 4mm cable and 20 A protection on 2.5mm cable after the garage consumer board.
well, as regards assessment, i would explain that you realise that there is no discrimination, but lacking a hi-integrity CU, that's the best you could do .
Providing that you're not on TT earthing and that the cable to the garage is armoured or surface run, then you don't need the RCBO at the house end. Change it for an MCB.
No offence intended, but you need to start thinking what's actually required rather than just doing what's "standard".
Reactions: 1 person
Hi
No such thing as double protection, more like pain in the bum I'll never know which RCD has tripped. Like that it won't comply and thats not good for an assessment...?
Reactions: 1 person
At least being an RCBO you wouldn't affect the rest of the installation. I've noticed over the years that many people with a fully RCD protected CU take the supply out then add another RCD in the outbuilding, and to be honest I've never known it to be that much of a pain unless someone very accident-prone lives there :-)
True!
Just not the way to do it, but. ..... true. Seen loads.
Agree entirely Spartykus, tho if the worst I saw on my travels was an extra RCD in the circuit I would be a happy bunny :-)
Reactions: 1 person
Yeah happy days point taken just going to keep it on a 32A breaker at the main board and it is covered by RCD in the garage so happy with it!
Run from house to garage less than 3 metres
Height more than 3.5 metres
All the measurements are fine.
Fair one, just had 12 years of sparky stuff in the forces takes a bit of time to get used to all these regs and assessments but yes cause it is protected by an RCD at the garage will just have it on a 32A MCB at main board. Cheers for help!
One point if your trying to impress the assessor. I know the 3m unsupported is in BS 7671. However I always support them. A catenary is only a few quid and it makes the job more professional. We`ve all seen damaged unsupported cables even over <3m.. Just a thought.
Reactions: 1 person
Double check for Elecsa assessment job
ELECSA Certification Scheme
Certification NICEIC, NAPIT, Stroma, BECSA Forum
hutch6447,
hutch6447,