Ah i see! It does look like a combined leakage, that rcd is tripping at an awful low value too, try replacing itNo because they can have the washer working if the dishwasher isn't plugged in..but not at the same time... So everything on apart from washer, put washer in - trips. Everything on apart from dishwasher, plug dishwasher in and it trips.... This is why I'm think combined earth leakage is tripping faulty rcd? It's bizarre to be honest!
If it is combined leakage how can this be solved as the main switch is the rcd. The reason im being so cautious is because this job is 150 miles away from me (go where the work is) so I need to go armed with everything and the kitchen sink!Ah i see! It does look like a combined leakage, that rcd is tripping at an awful low value too, try replacing it
First you need to find out what the leakage is, i would replace that rcd too because if it ramps at 19mA thats very low for a 30mA rcd, 24-27 is what you should be looking for. If it is higher than that you may have to split the circuit onto seperate rcd's or use high integrity earthing at socket outlets.If it is combined leakage how can this be solved as the main switch is the rcd. The reason im being so cautious is because this job is 150 miles away from me (go where the work is) so I need to go armed with everything and the kitchen sink!
MK LN 5780 80 AMP 30mA OLD STYLE RCD CIRCUIT BREAKER. | eBay This link is the rcd, as you can see its an old one....I need to get this right on the day so as much help as poss is very much appreiate.. Thanks again everyone! I'm still open to ideas by the way haha!!
I disconnected my circuit totally from the board and tried to get rcd results and Zs results but the rcd was tripping straight away... I'm going back next week with an earth leakage meter and try again.. Thank you.
Here we go again, leave a disconnected circuit (that you have altered) over the weekend.
Do you have any sense of professional pride? Obviously not, the Friday night pint is so much more important, isn’t it?
You’re name will be mud within you’re customers circle of friends, bad news travels 50 times faster than good.
Tony, with respect, have you read this thread through its entirety? best that you do, then make a comment.
I’ve spent all my life in heavy industry.
It’s OK. We'll leave the plant shut down until Monday and I’ll sort it then.
I have never walked away from a job. I warned my (then future) wife, don’t think I will be back home at the end of every shift.
A 38 hour shift? I couldn’t/wouldn’t go home until things were running again.
OK I was paid well, but I was on a salary so didn’t get any extra. “It was expected!”
Sorry, but our ethics may be different.
Hi all,
Just wanted to let everyone that replied to my post that it is now solved! The problem was a faulty RCD. I got there this morning and ramped tested the RCD at the board with all the circuits switched off and got a reading of 15mA. I changed over the RCD, ramp test that and got 27mA
Got disconnection times of 28.8 x1 and 9.7 x5 and a Zs of 0.48. Obviously all appliances are staying on too, so customer can have washer and dishwasher running at the same time, all good!
Just a quick question - do you guys do a full installation test before you start any alterations? In hindsight this would probably spotted the problem before I started any work and I am now considering doing full testing before hand!
Thanks for your help on this subject everyone!