Not amendment 3 compliant as the board is made from a combustable material.

My thinking behind the rating for the tails is, the supply cut out fuse is a higher rating than the 16mm tails. No sign of overloading or thermal damage.

The quote the reg number you feel it doesn't comply with, not just the whole damn book! What combustible material is the board made of? You said it's a 3036 board and the vast majority of them were pretty damned incombustible, especially the wooden backed ones.

what I said the actual loading on the tails? For a two bed cottage you're unlikely to see more than 20A so 16mm tails really shouldn't have an issue. Have you confirmed that the fuse is 100A?
 
Using "ammendment 3 compliant" is poor terminology and you should be referring to the enclosure construction which is as you say is of combustible material but I personally wouldn't Code this at all but some people may.
I would code 3 it if the db was under the stairs or in an escape route to the property, hallway next to the front door for example.
 
The quote the reg number you feel it doesn't comply with, not just the whole damn book! What combustible material is the board made of? You said it's a 3036 board and the vast majority of them were pretty damned incombustible, especially the wooden backed ones.

what I said the actual loading on the tails? For a two bed cottage you're unlikely to see more than 20A so 16mm tails really shouldn't have an issue. Have you confirmed that the fuse is 100A?

Fair comment on the reg number, do you do that for every code?

Its a plastic board. Not quite sure what you mean by the wooden boards being damn near incombustible, when wood is very combustable?

The loading on the tails is minimal.

Just from the sticker on the cut out fuse. How else can you prove it? Im not contacting the DNO as this is just for practise.

Thanks for the help
 
Fair comment on the reg number, do you do that for every code?

Its a plastic board. Not quite sure what you mean by the wooden boards being damn near incombustible, when wood is very combustable?

The loading on the tails is minimal.

Just from the sticker on the cut out fuse. How else can you prove it? Im not contacting the DNO as this is just for practise.

Thanks for the help
It would be a limitation on the eicr if the fuse size is unknown.
 
I always put the DNO fuse as "Not Verified" on an EICR. What make is the board some of the Wylex boards are of wood frame construction. So where and why are you practising this on?
 
Maybe you should have supplied more information initially. The amount of people who come on here asking what side to butter their bread on is unbelievable.
One question, how have you decided none of the sockets will supply equipment out of doors, check in the shed for a lawnmower :)
Whichever side you do decide it still ends up butter side down when you drop it.
Sods law
 
Im not doing the actual EICR, Ive just done it for practise.

But am I sure whether I should be doing EICRs, with enough experience, yes. But I didn't come here to discuss my competency with yourself, I came here for advice.

type of supply TN-S
Fuse type BS88 GG 100A
small two bed cottage
No sockets to supply outside equipment

Any thoughts would be appreciated.
Have you verified the characteristics of the protective device? If not, how can you code the tails.

I wouldn't code the CU.

Why are you coding the lack of RCD protection as C2?
 
Since when it was installed it was up code unless the install has become dangerous since then would it be c3 with an advisory? Or no code?
Still an apprentice so don't do eicrs just curious.
 
Ok Lumie, you have ( unintentionally ) poked a hornet's nest with a big stick.
It would have been helpful if, as part of your OP, you had explained this was a hypothetical question, that you don't carry out EICRs and that you are just trying to get your head round how certain things might be coded....then some of the responses might have been more moderate.

No harm in asking questions, that's hopefully one of the ways we all learn, but you must explain the context of your question.
Now, you probably have the answers you were looking for..
- a CU with rewireable fuses will not necessarily attract any code ( hardwood or plastic), but it may do.
- no rcd protection may not attract any code, but it could also be a 3 or 2 depending upon the particular situation.
- 16mm tails on a 100A BS88/1361 may only receive a comment if the max demand is lower that the ccc of the tails.

What you will have learned is that coding will depend on several/many specific factors and you need to be aware of them all, as well as the specific regs you believe are being broken, before you start allocating codes. And to do EICRs professionally, you must have an above average understanding of BS7671!
 
Fair comment on the reg number, do you do that for every code?

Its a plastic board. Not quite sure what you mean by the wooden boards being damn near incombustible, when wood is very combustable?

The loading on the tails is minimal.

Just from the sticker on the cut out fuse. How else can you prove it? Im not contacting the DNO as this is just for practise.

Thanks for the help

Yes of course you quote regs, you can't code things that aren't in the regs.

The wood is treated to be fire retardent, just try getting it to burn!
The plastic used in those days wasn't particularly combustible.
 
Which regulation mentions the location of the CU being a deciding factor?
Comes form the NICEIC examples of codes.
I sought guidance as to what to code this if any from an area inspector.
If the db is in an area of sole means of escape but has no signs of thermal damage or loose connections c3.
Now you can argue with this statement all you like but I do see where it comes from.
As bs 7671 calls for non combustible materials to be used or a cu to be installed in a non combustible enclosure, I don't think it's unreasonable to c3 it in an escape route of a dwelling.
Final coding is down to the inspector as the buck will stop with him.
As you know a c3 is still a satisfactory outcome just an improvement of the overall safety and nothing more.
 