Whereabouts in GN3 is it 'bandied about'?
There is a figure of 0.05 given as a suggested maximum value for the resistance between the cable termination at the bs951 clamp and the pipe itself.
good post. that 0.05 figure is misunderstood by so many sparks as being a max. value for the resistance of a main bonding conductor.