Whereabouts in GN3 is it 'bandied about'?

There is a figure of 0.05 given as a suggested maximum value for the resistance between the cable termination at the bs951 clamp and the pipe itself.

good post. that 0.05 figure is misunderstood by so many sparks as being a max. value for the resistance of a main bonding conductor.
 
I meant the rest of the installation was satisfactory - It was not a pile of mince. Usually by the end of a 100% EICR you get a pretty good idea of the quality of the install.
Cheers
 
Garry,I think my approach would mirror tels post

The installation is of a good standard,the bonding cables exist at the consumer unit,the continuity test would ensure they were connected to the service they were intended for
Given the positives that you have stated I think it is a bit of over zealous to expect the installation to be considered potentially dangerous by coding it 2 but its your opinion that matters
 