Hi,

My friend has just had EICR test done on 3 bedroom house. 5 year old house.
The house failed on - bathroom light under 2.25m inside bathroom zone with inadequate ingress protection.
The cost for the assessment was £180.
I am qualified in NVQ 3, HNC in Electrical Engineering. 17th edition amendment 3 BS7671.
I can sort the light. However, my friend has been told after the repair it will need to be re-assed at another cost of £180.
Is this how it works to charge again if you have failure and the electrician has only the failed part to check.
Comments / advice are welcome.
 
No way should you have to pay another £180 to the same company , pay for the repair and that’s it

£180 for a full eicr is quite cheap thou so perhaps they realise thay messed up charging so little and now trying to claw some money back

a full Eicr 8-12 circuits is normally around £250-300
 
The EICR will remain unchanged after the fitting is replaced, unsatisfactory not failed. Ask for a Minor Works Certificate which is proof of the works being rectified.
 
Hi westward10,

I am not self employed electrician so I cant provide Minor Works Certificate.
I work for the NHS as electrician. Unless I have read your reply wrong.
Thanks
 
If this is a rental property the agent will require proof of the works being carried out.
 
Yes it is rented property. Empty at the moment. New tenants waiting to move in.
So, would I be correct in saying the landlord will have to pay the £180 again to get signed off.
Thanks
 
Hi westward10,

I am not self employed electrician so I cant provide Minor Works Certificate.
I work for the NHS as electrician. Unless I have read your reply wrong.
Thanks
Anyone can provide a minor works cert. as long as you have the knowledge to do the work correctly, the appropriate test equipment and a certificate to fill out. you are good to go.

The only thing you should be wary about if you are doing this on the side as a favour is that you may not have the correct liability insurance to back you up if there was ever a problem in the future.

Remember, you dont have to give the work to the guys that did the report, and you dont need to get a new report done after it has been repaired, just keep a record of the repair on file.
 
Hi,

My friend has just had EICR test done on 3 bedroom house. 5 year old house.
The house failed on - bathroom light under 2.25m inside bathroom zone with inadequate ingress protection.
The cost for the assessment was £180.
I am qualified in NVQ 3, HNC in Electrical Engineering. 17th edition amendment 3 BS7671.
I can sort the light. However, my friend has been told after the repair it will need to be re-assed at another cost of £180.
Is this how it works to charge again if you have failure and the electrician has only the failed part to check.
Comments / advice are welcome.
 
Hi James,

I dont have liability insurance.
I am looking to get my 18th Edition and part P. As well as liability insurance. looking around for course costs.
Looks like the landlord will have to get self employed electrician to repair the fault who has liability insurance.

Thanks
 
Hi James,

I dont have liability insurance.
I am looking to get my 18th Edition and part P. As well as liability insurance. looking around for course costs.
Looks like the landlord will have to get self employed electrician to repair the fault who has liability insurance.

Thanks
liability insurance only covers you for causing damage. nothing to stop you replacing the light and filling in a MWC. you should be able to test the circuit . Zs and RCD trip times should be recorded. and in any case, it should only be a C3 on the EICR (improvement recommended, not unsatisfactory).
 
Hi,

Telectrix replied it should have been C3 and not C2.
What is the process for raising these type of disagreement to the company who carried out the testing.
What evidence can I provide.
 
You could photocopy of 465 of your 18th edition regs book as that has one version of a minor works certificate on.
Or there is an editable one on this webpage apparently.
 
Hi,

Telectrix replied it should have been C3 and not C2.
What is the process for raising these type of disagreement to the company who carried out the testing.
What evidence can I provide.
Depends where the light fitting is inside/outside the zones, depends on the IP requirement, and therefore the C2/C3 Coding!
 

Reply to EICR test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
489
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
809
I paid an electrician for an EICR test - two of his men took 3-4hrs to do the test. This was on 28/04. He since told me that the test failed and...
Replies
11
Views
2K
Hi, recently had an EICR test done by 'Landlord Certificates' which failed due to circuite 3 having two radial circuits into a single 32amp MCB...
Replies
31
Views
4K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
671

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock