Hello,
I have following scenario, 20A circuit breaker in the CU. 3 x 2.5 SWA cable feed to a garden shed CU. In the shed CU I have 0.69 ohm on the income cable. On the shed are two 16A radial circuits of socket outlet. When I do Ze on the sockets , I get 2.9 ohms.
The radial circuits have 2.5mm2 flat cable no longer than 5m from the shed CU.
Any idea why is the reading so high please?
 
is there a RCD in shed? this could cause a high reading if using no-trip EFLE test. try doing the test this way to eliminate the possibility. ( use the hi-current 2 lead test ).

High current Zs test with RCD.jpg
 
Hello,
I have following scenario, 20A circuit breaker in the CU. 3 x 2.5 SWA cable feed to a garden shed CU. In the shed CU I have 0.69 ohm on the income cable. On the shed are two 16A radial circuits of socket outlet. When I do Ze on the sockets , I get 2.9 ohms.
The radial circuits have 2.5mm2 flat cable no longer than 5m from the shed CU.
Any idea why is the reading so high please?
What do you mean "I have 0.69 ohms on the income cable, and Ze at the sockets"???????
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
elec. power to a garden shed
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
42
Unsolved
--

Advert

Thread statistics

Created
ondro,
Last reply from
Dave OCD,
Replies
42
Views
3,922

Advert

Back
Top