Working on a self contained emergency lighting system.

There are 70 emergency lights over 3 floors.

The emergencies are wired on a separate circuit from the local lights but fed from the same DB.

I require the supply for the self contained (batt back up) lights to disconnect, when theres a disruption to the local lighting circuit.

My plan is to achieve this switch over with X 2 20A, 2 pole contactors with 240V coils (one for local lighting, one for emergency lighting)

Can I supply the contactor control circuit from the local lighting circuit, so when it trips/fails it opens my contactors & cuts power to my emergencies, bringing the batteries into action.
 
You could, but why not just move the emergency circuit to the same circuit breaker as the local lights? You could put a test switch next to the dB.
 
  • Like
Reactions: Flanders
Surely the emergency lighting covers more than one general lighting circuit per floor. Swap them all for maintained.
 
That's not a good idea, the contactor will be energised near 24/7 so will burn out pretty quick.
 
Hi Everyone.

Working on a self contained emergency lighting system.

There are 70 emergency lights over 3 floors.

The emergencies are wired on a separate circuit from the local lights but fed from the same DB.

I require the supply for the self contained (batt back up) lights to disconnect, when theres a disruption to the local lighting circuit.

My plan is to achieve this switch over with X 2 20A, 2 pole contactors with 240V coils (one for local lighting, one for emergency lighting)

Can I supply the contactor control circuit from the local lighting circuit, so when it trips/fails it opens my contactors & cuts power to my emergencies, bringing the batteries into action.
Dell you could do just by adding one 2 pole relay 1- NO 1-NC contacts
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Emergency Lighting contactor switch over
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Delectrician,
Last reply from
Delectrician,
Replies
5
Views
4,414

Advert