S
Stroppy
be nice and earthy, though, with all that water around!
You see that's where we completely differ, your all too willing to put your faith in RCD's instead of making the effort to have a TT system work as it should!! You may well install an S type up-front, to cover any down stream RCD's, but lets be honest now, ...how many UK electricians, let alone so-called DI's would even think about installing one?? Most of them are convinced that RCD's are as reliable as MCB's so why would they bother!! Again, having so easily obtained a 15 ohm reading, means that your ground conditions are pretty good, (and that the existing rod is probably a twig that hasn't been installed properly) so i'd of put a little more effort into the system. Who knows, that TN value could well have easily been realised!! lol!!
To be totally honest, i don't really know why you bother installing a TT system if that's your honest view. If your not bothered about Ra values and the importance of stability, why not just add your RCD's and let any bonding to the installation be your reference earthing. Using your argument the 700 ohm Ra from the existing rod is as good as any, it's under your magic 1667 ohms ...lol!! All in all, it's a sad day, when other international earthing standards can teach the UK a thing or two, especially when in many cases, their standards are actually based or taken on/from past British standards!! Personally I'm happy to install to Bs 7671 regardless of whether or not you agree with it.The reason for upgrading the 700 ohm reading was it was picked up on an EICR by myself as not complying with the recommendation in Bs7671,and coded 3. With a functioning RCD it was perfectly safe and did not represent a dangerous situation,improvement only needed to bring it within the 7671 spec. That is the only purpose of an EICR,picking up things which do not comply with 7671....not the regs according to E54.
On all the projects i've ever been involved on, i can't think of a single one where the specifications didn't call for any earthing system to be higher than 1 ohm. That value covered TX installations, as well as other made earthing systems... and your trying to defend your Reg's and it's 200 ohms!!!! ....Quite amazing!! I think most of the projects you are involved in are much,much larger than the TT systems commonly discussed on here....which are very small scale,such as sheds,single dwellings,garages etc.
As the old saying goes, ...you can lead a horse to water but..... lol!!
I must have missed this post!!
Most, if not ALL will be, on a domestic installation if i'm not mistaken!! not correct...only since 2008 has it become the norm for blanket RCD protection,the majority of UK installations are pre-2008.
Clearly not right, but still protected by a RCD with it's magic 1667 ohm Zs, so complies completely with your analogy!!
All depends what you mean by ''slightly exceeded'' replacing a type B with a type D MCB and the difference can be substantial!! And if Zs values don't comply, then disconnections times will be extended!! But again, no problem we have a RCD to cover it!! lol!!Bang on the money mate.....glad you are finally beginning to see the light.
I reckon TT systems should be outlawed and everything made TN.
To me it seems archaic and unreliable expecting something as important as fault current to somehow dribble its way through soil, rock, sand, concrete, and whatever other crap lies between an installation and its transformer, when there is a perfectly good neutral connection going back to it anyway, which doesn't get worse or disappear in hot weather.
I reckon TT systems should be outlawed and everything made TN.
To me it seems archaic and unreliable expecting something as important as fault current to somehow dribble its way through soil, rock, sand, concrete, and whatever other crap lies between an installation and its transformer, when there is a perfectly good neutral connection going back to it anyway, which doesn't get worse or disappear in hot weather.
So tell me, what do you think gives a DNO Distribution Transformer it's earth and it's TN-S cables earth and PME / (TNC-S) neutral conductors it's multiple earthing then?? lol!!
A local stable TN value TT system is better to have, than a supplied TN earthing system. You are in control of that system not others!! Yet many of you scoff at the idea as not being possible, when in fact it's more than just possible!! Though you certainly wouldn't think so, going by this thread and the ''why bother'' attitude!!
The seemingly total lack of understanding towards TT systems in the UK these days, is just amazing!!
THAT is exactly what the lecturer at the college said when I was doing the 2391 course.
Then he spoiled it by saying if you're fitting an outside halogen floodlight which has to be earthed and there's no cpc in the cable, you can link the earth terminal to the neutral at the light ............
Haha, wonders never cease to amaze me!!
So what are you saying here, that a project's TT earthing system is different in importance to that of one of your domestic customers (and i'm not talking about sheds!!)?? No way on this earth would i ever see the type of light yor talking about!!
Of course your happy to conform to BS7671, it means you don't have to think about anything or come to that do much about anything either. So in your world an existing useless 700 ohms is worth changing to an equally usless 200 ohms because it says so in the Regs,yep and all because you have an RCD in place??yep Which just about sums up your argument!! That and this existing 700 ohm being perfectly safe, yeah right!! yep Why even consider the fact that the all singing, cover all RCD is going to fail sooner, rather than later....nope
Can't really be arsed anymore, you'll only come up with another smart arsed reply yep that is just going to be, yet another compromise for a working TT systemnope. I'm just wondering if you have ever installed any TT system with a sub 1 ohm or TN valuenope, perhaps before RCDs became the norm?? Probably not, definately not as you still wouldn't see the point and come up with some compromise or other!!yep
Come to that, Do you really install an S type up front on your TT installations??new ones...yep Because from your posts on this thread, Frankly i can't really see you bothering, and just using them as an example, to get over the other argument, of totally relying on a single RCD sitting on a numbty Ra value!!
new ones...yep
They always spoil things!! Why would you even think about installing a circuit without a CPC these day's!! lol!!
Many reasons, the biggest one I can think of being distance.
I guess lol. Erm, ok, there's not very likely to be a reason to install a cable with no CPC in a domestic. How's that![]()
Well, we were talking about a domestic!! But then why would you install a cable(s) that didn't include a CPC??
Good point, I hadn't thought that far ahead. Was just having a rant. I don't think we did distribution transformers on my 5 week course, although that may have been in the two weeks I was off having it large in Ibiza. Can't have missed that much.So tell me, what do you think gives a DNO Distribution Transformer it's earth and it's TN-S cables earth and PME / (TNC-S) neutral conductors it's multiple earthing then?? lol!!
A local stable TN value TT system is better to have, than a supplied TN earthing system. You are in control of that system not others!!